MikeGuerard

Member
Join Date
Jun 2016
Location
Ottawa
Posts
21
Hi Guys,

Just looking for a bit of help understanding an issue on two of our newer machines:

Running AB 1756-L73S 5570's with V21
Motion Group is Kinetix 6000's with 2094 amps. (Sercos)

Each time we download a new change to the program, the motion group's "GroupSynced" bit drops out.

A power cycle to the PLC is required to get things aligned again.
No faults flashing on any of the Kinetix drives.

Within the logic, we use the GroupSynced bit as a permissive to enable the amp power, so this essentially pops up a slew of faults for all servos.

I'm not seeing much in the way of help from AB on the KnowledgeBase articles, except for #29240, that specifies V12/V13 of Logix.

Any insights?
Is there an easier recovery method than cracking an electrical cabinet to power cycle the PLC?

Thanks in advance.

Mike
 

Similar Topics

I have to start out by saying I am not a PLC programmer and I have basic programming skills but mainly use software as a troubleshooting tool. I...
Replies
0
Views
120
Good Afternoon , I'm sure there are many Ishida Muti-Head Weigh Systems . We have a Ishida CCW-M-214W Multi-Head system . We are...
Replies
1
Views
508
Kindly, we have the following faults with a Kinetix 5700 servodrive. We checked the encoder cable, but found nothing damaged. What could be...
Replies
1
Views
264
Hello! We are using a ControlLogix 1756-L72 PLC with two identical servo motors running separate conveyor belts. The machine this is on runs...
Replies
4
Views
959
First time poster and somewhat new to PLC programming. I own a brewery, have a programming background, and one of the machines on my canning line...
Replies
2
Views
963
Back
Top Bottom