Using an external HIM such as 22-HIM-C2S or 22-HIM-A3, HIM copycat is an available option for backing up and restoring PowerFlex 525 parameters. There’s no such option on the built in control module HIM.
If the only HIM Copycat selection you see is copy from device to HIM, there is no saved parameters set in the HIM. Go through the system and save parameters to the HIM's so you have them for the future. I suggest take the time to name each one so you would know if HIMs got switched. Pressing the number / navigation buttons while letter scrolling will jump through characters to save a little time holding up or down. Zero jumps to the blank space.
All the built in 525 parameters including onboard IP are covered in one save. I expect an add-on comm module is a separate save but I haven’t used one. I know it’s a separate save on PowerFlex 70. If something besides the HIM and drive shows up in the HIM menu for device select, I expect it’s a separate save. Cycle power to reboot with new settings after writing from HIM to drive.
Provided the control module is OK and only the power module has failed, you *should be able to run a new power module with the old control module. I have seen an alert for firmware mismatch between modules and *IIRC, it still worked. We only swap modules like this temporarily in a pinch because then both pieces wouldn’t be fresh and our cost difference is minimal between a complete drive and power module only.
A common USB-B will connect to the control module once removed from the power module. It should show up as a USB memory stick with the utility installer there. It might even be a stand alone executable that doesn’t need installed. That’s another means to backup and restore parameters.
Parameters can be saved in the Logix/Studio 5000 project. If drive parameters are already saved with the project, you would go online with the PLC, open that drive in the I/O tree, and download to the new drive from there. If they’re not saved, get them saved if you can.
Parameters can also be saved as a multiple drive project or each drive as an individual project using CCW. Ethernet is the usual connection for that but you could connect with a 1203-USB or similar device.
ADC is automatic configuration of the drive that I haven’t seen used much. A managed switch that assigns IP by port is sometimes used so you don’t even have to set the IP manually. If you really hate yourself or others, try DHCP.
An alternative to ADC could be a scattered write in the PLC program, after IP is set manually or by port. That should be triggered only as needed. Continuous writes would burn out the ROM.