PF525 Head Scratcher

I wired up a replacement Reliance drive years ago, we got a 15hp instead of a 10hp as that was all they had in stock, put all the parameters in (we had a second machine that used the same drive so got the parameters from that).
When it tried to run it would come up with a overcurrent, bypassed it to get the machine running (the VSD was only there to convert 50Hz to 60Hz for a cooling fan), Rockwell came the next day and that's when we found out that the 10hp had the supply terminals on the left side and the 15hp had them on the right side. But no smoke came out.
Also I have seen PowerFlex 700H drives wired the wrong way and power up OK.
Not sure about PowerFlex 70's or 750's, I have not seen any of those wired the wrong way.
 
Not sure about PowerFlex 70's or 750's, I have not seen any of those wired the wrong way.


If dealt with 1 PF755 that were the motor and power leads were swapped. After correcting the wiring, it powered up OK but then exploded that instant i started the direction test. I'm really glad it was a small drive.
 

Similar Topics

I seem to be on here often lately but cant find specifics about my situation I am trying to control the drive using both ethernet and analog(for...
Replies
1
Views
747
When E300 powered off, the ethernet device tag data stayed at last know state, for example, fault bit is still Off, ready bit is still ON, status...
Replies
8
Views
1,009
Hello all, New to this site - I am adding a new conveyor and using a powerflex 525, though the rest of the drives operating this line are...
Replies
7
Views
1,282
I have a (*) PowerFlex 525 being supplied with 400VAC, 60 cycle, 3-phase. This is not a type-o, this is accurate. Now, the drive clearly states...
Replies
3
Views
1,179
Has anyone had any success using a PanelView Plus to directly control a PF525 over ethernet, I tried to use the file provided with TechNote...
Replies
1
Views
1,060
Back
Top Bottom