Redundent OPC servers to an OPC client

Ibot26

Member
Join Date
Jun 2022
Location
Minnesota
Posts
1
Hello,

I am trying to connect kepServerEx v5 in parallel with RSLinx Classic lite but kepserver will not connect to the PLC if RSLinx is active and vis versa. Can you have more than one OPC server connected to a plc (L62)?

Does RSLinx classic lite have an OPC tag limit?

Thank you
 
Last edited:
You can have as many OPC server as you want talking to PLC. Widelto is right, RSLinx lite will not act as an OPC server but that's beside the point. I don't see how RSLinx would conflict with kepware even if you have a paid version of RSLinx working as an OPC server.

You have to put in much more detail; what do you it will not "connect". Screenshots will help.
 
Are Kepware and RSLinx on the same node? This could create a conflict.

Check available CIP connections in the PLC, either server connected may be running you out of available connections.


FYI - RSLinx licensing parameters:

RSLinx Lite - not licensed for OPC server features

RSLinx Single Node - allows one LOCAL OPC client, connecting to one device. Client must connect using OPC in-process (IN-PROC) mode. No other OPC clients will be able to connect.

RSLinx OEM or PRO – allows one LOCAL OPC client to connect to multiple devices. Also must be IN-PROC. No other OPC clients will be able to connect.

RSLinx Gateway – allows multiple local or remote OPC clients to connect to multiple devices. Client must use out-of-process (out-of-proc) connection
 
I forget, vnpmoose is right. An OPC might take out a "connection" and there are only so many of those available on a Logix PLC.
 

Similar Topics

Dear All, My config as follows. - 1 pair of Redundent WinCC - 1 WinCC Client - OPC XML DA installed on client - MES will access Wincc Data...
Replies
0
Views
3,151
Dear all i oome to find that my master cpu all leds is flashing and as per manual this means that CPU is faulty so can u advise, is it...
Replies
1
Views
2,344
dear all experts one day i found that the master cpu's all leds is flashing and control transfered to the slave one after trouble shooting the...
Replies
1
Views
3,078
i have two plc slc5-05 1747-L553 and 1747-bsn backup scanner my quastion , how i can transfer data table between two plc ?
Replies
0
Views
1,437
I am running CCW 13 trying to upload to a micro 820 vers.12 I get an output message OPC server is unable to load project controller. Please help!
Replies
1
Views
105
Back
Top Bottom