Hi, I am sure it must be simple but my head is not working at the time.

I have
- Encoder pulses (Input)
- Pulse per Rev of the belt
- Belt circumference (mm)

mm_per_rev = (Belt circumference/PPR)

I am calculating distance d (m) = (Pulses) x mm_per_rev/1000

Question is how to calculate the speed?
I must have all this within AOI so cannot use time based routine to calculate the speed. But ms pulse is provided for AOI.

it must be something like
d2 - d2 / t2 - t1

what about rollovers etc.
Appreciate your help.
 
Speed = [distance traveled during last elapsed time] / [elapsed time]. If you calculate for example velocity every 5 seconds, then the velocity in m/s will be just the traveled distance divided by 5.

Rollover : if the total distance is for example >= 100000 then subtract 100000, then the traveled distance will be negative and to correct it just add 100000
 
Convert Speed units per scan speed to per second

Actually I am looking to convert speed units per scan which I am obtaining from differential distance to speed (m/s).šŸ™ƒ
 
To obtain a stable speed reading you need a precise time base, and the scan time of a PLC is not usually stable.

In addition you need to count an appreciable amount of pulses between measurements, I think there should be at least 50 pulses
 
To obtain a stable speed reading you need a precise time base, and the scan time of a PLC is not usually stable.

In addition you need to count an appreciable amount of pulses between measurements, I think there should be at least 50 pulses

If you put your speed calc code in a Periodic Task the scan time base will be precise. We do it all the time.
 

Similar Topics

Hi everyone, This is my first time posting, so please forgive any omissions or mistakes. I am attempting to control the velocity of a stepper...
Replies
18
Views
750
Hi; We have 5ppr 12vdc encoders (06nos) available in stock which I want to use at a machine to upgrade it. But Fatek PLC, which I want to use...
Replies
2
Views
1,587
Hi Everyone! i'm a newbie to PLC And i have a question, How do i count pulses from a encoder giving positional feedback? my plan is to use this...
Replies
5
Views
1,649
Hello everyone! I have strange problem. I have plc, inverter (mitsubishi), incremental encoder (sick) and motor. When i set the frequency on the...
Replies
8
Views
3,921
Hello. So we have a machine with a carriage run by a VFD driven motor. I have noticed that for some reason it periodically loses 720 pulses and...
Replies
7
Views
2,879
Back
Top Bottom