Book Two different power sources in 1 control cabinet

Hello all,

We have an electrical cabinet which powers an okuma machining center (OMC) and also includes i/o module for robot. All devices related to OMC is powered from 480V, which is stepped down to 120V (NPN), which is then stepped down to 24V (NPN). The main breaker / disconnect is tied to the 480V 3 phase coming in.

Looks like few years down the line, they added a fanuc robot in front of the machine, so it was necessary to install an i/o module inside the same cabinet. However, for some reason, this was wired using PNP setup. So someone added a separate 120V power supply inside the cabinet, which is then stepped down to 24V pnp. The 120V is not connected to any switch / breaker, there are only fuses. It is actually coming from a power outlet next to the machine.

From my understanding, the idea was, in case the OMC went down, the robot i/o module was still powered on, and the robot could still run.

My task is to eliminate the safety issue where if someone turns the breaker off, they may assume there is no power in the machine, when actually there is still 120V / 24V pnp for the robot i/o module.

So I have figured out the wiring, and I can re-wire the robot module circuit to get fed by the original 480V coming in, so everything inside the panel would be tied to the OMC main breaker, but would lose the advantage of having the robot running in case the machine goes down.

Is it considered good practice for me to add a plexi-glass covering with holes around the robot i/o module power supply, and maybe change the wire colors to "orange" to showcase that power is still inside the machine, even though the main breaker is off? I want to figure out a way to keep the robot alive, even if the OMC breaker is turned off. I don't want to create a separate panel / junction box just for the robot i/o module power.

The reason I have recommended this idea, is I have seen something similar on different machine, were they used orange cable to denote power was still on the machine (it was backup battery for computer)

Any ideas are appreciated. Thanks,
  Reply With Quote
Unread November 19th, 2019, 04:43 PM   #2
thingstodo
Member
Canada

thingstodo is offline
 
Join Date: Feb 2012
Location: Saskatoon
Posts: 322
Quote:
Originally Posted by alive15 View Post
Hello all,

We have an electrical cabinet which powers an okuma machining center (OMC) and also includes i/o module for robot. All devices related to OMC is powered from 480V, which is stepped down to 120V (NPN), which is then stepped down to 24V (NPN). The main breaker / disconnect is tied to the 480V 3 phase coming in.

Looks like few years down the line, they added a fanuc robot in front of the machine, so it was necessary to install an i/o module inside the same cabinet. However, for some reason, this was wired using PNP setup. So someone added a separate 120V power supply inside the cabinet, which is then stepped down to 24V pnp. The 120V is not connected to any switch / breaker, there are only fuses. It is actually coming from a power outlet next to the machine.

From my understanding, the idea was, in case the OMC went down, the robot i/o module was still powered on, and the robot could still run.

My task is to eliminate the safety issue where if someone turns the breaker off, they may assume there is no power in the machine, when actually there is still 120V / 24V pnp for the robot i/o module.

So I have figured out the wiring, and I can re-wire the robot module circuit to get fed by the original 480V coming in, so everything inside the panel would be tied to the OMC main breaker, but would lose the advantage of having the robot running in case the machine goes down.

Is it considered good practice for me to add a plexi-glass covering with holes around the robot i/o module power supply, and maybe change the wire colors to "orange" to showcase that power is still inside the machine, even though the main breaker is off? I want to figure out a way to keep the robot alive, even if the OMC breaker is turned off. I don't want to create a separate panel / junction box just for the robot i/o module power.

The reason I have recommended this idea, is I have seen something similar on different machine, were they used orange cable to denote power was still on the machine (it was backup battery for computer)

Any ideas are appreciated. Thanks,
I would add a local disconnect, a 6 pole switch, between the 3 phase power to the first panel (3 of the contacts) to the OMC as well as interrupting the 120V feed to the robot power supply (1 contact). That is a positive lockout point for 'the whole thing', but under normal operation the 120V power would stay on during an OMC trip.

But perhaps I mis-understood the question
  Reply With Quote
Unread November 19th, 2019, 05:03 PM   #3
alive15
Member
United States

alive15 is offline
 
Join Date: Oct 2015
Location: al
Posts: 387
Book

Is that acceptable practice? To have two separate disconnects on the same panel for two different power sources? This would require two lockouts on the machine, instead of one. See my sketch?
Attached Images
File Type: jpg sketch.jpg (157 Bytes, 120 views)
  Reply With Quote
Unread November 19th, 2019, 05:05 PM   #4
alive15
Member
United States

alive15 is offline
 
Join Date: Oct 2015
Location: al
Posts: 387
See sketch on this link:
https://imgur.com/a/ZAUweOS
  Reply With Quote
Unread November 19th, 2019, 05:06 PM   #5
jimtech67
Member
United States

jimtech67 is online now
 
jimtech67's Avatar
 
Join Date: Jun 2002
Location: New Jersey
Posts: 391
no picture ... file size is most likely to big
  Reply With Quote
Unread November 19th, 2019, 05:09 PM   #6
jimtech67
Member
United States

jimtech67 is online now
 
jimtech67's Avatar
 
Join Date: Jun 2002
Location: New Jersey
Posts: 391
the 480 disconnect is separate from the the cabinet ???
Not integrated in to the cabinet ???
  Reply With Quote
Unread November 19th, 2019, 05:13 PM   #7
alive15
Member
United States

alive15 is offline
 
Join Date: Oct 2015
Location: al
Posts: 387
It's a 480V 3 phase cable coming down from a bus bar into the cabinet. You can unplug it outside the cabinet if you want. So even if you turn the disconnect off, there is still 480V 3 phase inside the cabinet, on the top side of the breaker. I don't even know if this practice is allowed also, seems weird to lockout the breaker, even though the 3 phase is still on the top and inside the cabinet.
  Reply With Quote
Unread November 19th, 2019, 05:16 PM   #8
alive15
Member
United States

alive15 is offline
 
Join Date: Oct 2015
Location: al
Posts: 387
There is not a separate junction box for the 480V. The disconnect switch is right next to the door of the cabinet. Old machine (20 years), maybe that was acceptable back then, I don't know about today.
  Reply With Quote
Unread November 19th, 2019, 05:22 PM   #9
jimtech67
Member
United States

jimtech67 is online now
 
jimtech67's Avatar
 
Join Date: Jun 2002
Location: New Jersey
Posts: 391
is the door interlocked with the 480 disconnect?

Is the disconnect with reach of the cabinet?
I am only asking because without seeing the set up it sounds like was done a long time ago and cludged together (i apologize if i'm wrong)..
I'm far from a safety expert or up on all codes but nowadays you have be very careful. If you touch it you own it.
  Reply With Quote
Unread November 19th, 2019, 05:54 PM   #10
James Mcquade
Member
United States

James Mcquade is offline
 
Join Date: Oct 2007
Location: Tennessee
Posts: 2,629
please refer to NFPA 79 - electrical standard for industrial machinery.

if you keep the additional 120 volt power, you will need the following
(2) voltage stickers for the disconnect power 480 and 120
(1) this enclosure has more than one source of power
(1) 120 volt sticker below the sticker just mentioned.

the external 120 volt wire color will need to be yellow or orange ( sorry, I don't have my copy with me) and also be finger safe.

i'm not sure of the current rules for dual power past the finger safe part.

hope this helps.
james
  Reply With Quote
Unread November 19th, 2019, 06:26 PM   #11
alive15
Member
United States

alive15 is offline
 
Join Date: Oct 2015
Location: al
Posts: 387
No, opening the door will not cut power off. Yes, the disconnect is right at the cabinet door.

I will go ahead and just add another disconnect, seems like the easiest and best option for me. I'll just require the techs to use two locks, and add the stickers as James mentioned. And change the red wire for 120V to orange color for the robot module.

Thanks!
  Reply With Quote
Unread November 19th, 2019, 07:48 PM   #12
bill4807
Member
United States

bill4807 is offline
 
Join Date: Mar 2013
Location: michigan
Posts: 164
Quote:
Originally Posted by James Mcquade View Post
please refer to NFPA 79 - electrical standard for industrial machinery.

if you keep the additional 120 volt power, you will need the following
(2) voltage stickers for the disconnect power 480 and 120
(1) this enclosure has more than one source of power
(1) 120 volt sticker below the sticker just mentioned.

the external 120 volt wire color will need to be yellow or orange ( sorry, I don't have my copy with me) and also be finger safe.

i'm not sure of the current rules for dual power past the finger safe part.

hope this helps.
james
This is what i was going to recommend as well.
Also add the second lockout location to your LOTO placard that should be posted on the machining center, for the new disconnect you install.

Most the time everybody wants the cell to keep running if 1 machining center goes down, so you try to keep it at externally feeding the I/O module in the CNC only at 24Vdc, supplied by the robot/cell PLC. Not supplying module power from the CNC.

But in your case it seems like they grabbed 120V and introduced it into the panel.
  Reply With Quote
Unread November 20th, 2019, 06:48 AM   #13
Rson
Member
United States

Rson is offline
 
Join Date: Jun 2017
Location: Michigan
Posts: 202
Current code is now Orange for wires that are not de-energized with the control panel's disconnect - no longer yellow. Of course, that depends on what NFPA your state is currently enforcing
NFPA enforcement map (scroll down half way)
Typically, use Orange with a red stripe for AC power from an outside source, and orange with a blue stripe for DC power from an outside source.

As mentioned above, if it is AC voltage, it probably should have a disconnecting means at the panel. If there is room, a disconnect inside the panel would work, or you can get an external disconnect like the ones below:
External disconnect enclosure
  Reply With Quote
Unread November 20th, 2019, 09:22 AM   #14
VAN
Member
United States

VAN is offline
 
Join Date: Apr 2012
Location: Wa
Posts: 287
Quote:
Originally Posted by Rson View Post
Current code is now Orange for wires that are not de-energized with the control panel's disconnect - no longer yellow. Of course, that depends on what NFPA your state is currently enforcing
NFPA enforcement map (scroll down half way)
Typically, use Orange with a red stripe for AC power from an outside source, and orange with a blue stripe for DC power from an outside source.

As mentioned above, if it is AC voltage, it probably should have a disconnecting means at the panel. If there is room, a disconnect inside the panel would work, or you can get an external disconnect like the ones below:
External disconnect enclosure
I thought the wire code had to do with the voltage not if it was always energized.

name the five colors associated with a 120/280V Y three phase panel - red, blue, black, green, white neutral

name the five colors associated with a 277/480V Y three phase panel - brown, orange, yellow, green, gray neutral
  Reply With Quote
Unread November 20th, 2019, 09:42 AM   #15
James Mcquade
Member
United States

James Mcquade is offline
 
Join Date: Oct 2007
Location: Tennessee
Posts: 2,629
Van,

is this your color standard or is there a code for these colors?

By the way, green doesn't always mean ground !
no, i'm not joking. my previous plant used green as 120 volt output wire because it was all they had on the weekend to get a machine running.
No, the wire did not get replaced. I found that out the hard way and lost the battle to replace the wire when I brought it up to the engineering manager.
it has been running for years and no one has complained yet was his answer.

james
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Allen Bradley 1769-L18ER-BB1B local 1734 point IO modules arrangements anirudhgk7 LIVE PLC Questions And Answers 11 November 11th, 2019 01:51 PM
Dynamic power control jsf1985 LIVE PLC Questions And Answers 14 September 8th, 2019 04:34 PM
SCCR , power supply & SPD questions for an industrial control panel - detailed mhismail LIVE PLC Questions And Answers 5 March 4th, 2019 02:12 PM
Confusion regarding power supply rating for CompactLogix Salman S. LIVE PLC Questions And Answers 8 March 7th, 2017 06:07 PM
PLC to manage renewable power sources jaraujo1 LIVE PLC Questions And Answers 4 September 16th, 2009 11:15 AM


All times are GMT -5. The time now is 08:41 AM.


.