Siemens BW500 belt scale reset total

Hey everyone,


Recently installed a Siemens BW500 belt scale on a conveyor, and everything is nearly wrapped up except that we can't seem to get Total 1 to reset using the PLC. I've followed the sample code that Siemens provides, including all of the bit swapping etc, but even forcing the Total 1 Reset output bit causes no change. The manual states that the reset won't occur until the bit goes from a 0 to a 1 and then set back to a 0, but that is happening in the logic to no avail. Does anyone have any experience or insight into this that might help?


Just for context, every morning at 6:59:59 AM we're performing a MOV to move the TOTAL_1 in the Milltronics to a different tag (TONS_PER_DAY_TODAY into TONS_PER_DAY_YESTERDAY) and then we use a TOF timer with a 200ms preset to trigger the OTE of the Total 1 Reset bit (E28_1350_SCALE:O.Data[8].0). I'll attach a screenshot below.


Thanks in advance!
Attached Images
File Type: png Capture.PNG (18.3 KB, 24 views)
  Reply With Quote
Unread November 14th, 2019, 11:06 AM   #2
peter764
Member
United States

peter764 is offline
 
Join Date: Oct 2008
Location: Maine
Posts: 22
Have you tried increasing your time on the TOF? A 200ms signal might not be long enough to reset the scale?
  Reply With Quote
Unread November 14th, 2019, 11:41 AM   #3
mylespetro
Supporting Member
Canada

mylespetro is offline
 
mylespetro's Avatar
 
Join Date: Dec 2015
Location: NS
Posts: 175
Quote:
Originally Posted by peter764 View Post
Have you tried increasing your time on the TOF? A 200ms signal might not be long enough to reset the scale?

We haven't, but I don't think that that's the issue in this case. The tech onsite said that he directly changed the state of the reset bit in the controller tags from 0 to 1 and then back to 0 and it didn't reset the total. I did forget to mention that we are using the SmartLinx Ethernet/IP card to interface between the scale and the PLC.
  Reply With Quote
Unread November 19th, 2019, 02:31 PM   #4
mylespetro
Supporting Member
Canada

mylespetro is offline
 
mylespetro's Avatar
 
Join Date: Dec 2015
Location: NS
Posts: 175
Hey everyone, resolved the issue. The onsite tech is familiar with Siemens and was saying that he thought we might have to set Parameter 799 from a 0 to a 1. This parameter is "Communications Control" and allows the PLC to write parameters, so our output bit wasn't being accepted until this was changed. Just wanted to give a heads up to anyone who runs into a similar issue.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Siemens or Omron? Gromit LIVE PLC Questions And Answers 35 November 14th, 2017 10:44 AM
Siemens S7200 Memory Reset Password Protected siemenssurplus LIVE PLC Questions And Answers 1 December 11th, 2006 03:55 PM
Siemens AI Modules Configurations Reset stevenPLC LIVE PLC Questions And Answers 2 October 7th, 2005 03:50 AM
Checking status of certain number of inputs dajody LIVE PLC Questions And Answers 7 October 10th, 2004 06:46 PM
Siemens S7 PID Reset input format Andy32821 LIVE PLC Questions And Answers 2 August 31st, 2003 01:49 PM


All times are GMT -5. The time now is 04:10 PM.


.