Hi all
I'm trying to add a Consumed Tag in a 1756-L63 across a EtherNet network to another 1756-L63 in a second chassis. I know the controller 1756-L63 producing the tags is working because there is a 1756-L1 consuming the same data in the same chassis.
I have the two Ethernet cards connected through a router and my laptop is connected wirelessly to the router for programming.
I'm getting a connection error (16#0203) Connection Timed Out on the 1756-L63 in the I/O configuration tree of the consuming controller.
My question is can I use an router or does this connection require a switch to connect between the two EtherNet cards. One card is a 1756-ENBT/A and the other is a 1756/ENET/B.
Also I made sure the producer had enough consumers.
I'm trying to add a Consumed Tag in a 1756-L63 across a EtherNet network to another 1756-L63 in a second chassis. I know the controller 1756-L63 producing the tags is working because there is a 1756-L1 consuming the same data in the same chassis.
I have the two Ethernet cards connected through a router and my laptop is connected wirelessly to the router for programming.
I'm getting a connection error (16#0203) Connection Timed Out on the 1756-L63 in the I/O configuration tree of the consuming controller.
My question is can I use an router or does this connection require a switch to connect between the two EtherNet cards. One card is a 1756-ENBT/A and the other is a 1756/ENET/B.
Also I made sure the producer had enough consumers.