Ab power flex 40 Modbus tag

Ramsri

Member
Join Date
Apr 2014
Location
coimbatore
Posts
40
Hi all,
I need to interface AB power flex 40 VFD with one third party HMI. I had look on the internet for AB Modbus Registers list & i found only few parameters. I have established the communication but which Modbus address is assigned for setting the frequency? In the internet, i have found 48193 address for Speed ref. But when i check for the same, i found it's a command source. Can anyone share me the details of speed ref. Modbus address in Allen Bradely powerflex 40.
 
Make sure that the drive parameter P38 is set to '5' to set the communication port as the source of the frequency command. You could also set appropriate bits in Modbus address 48192 to select the port.

We have typically found that the actual address entered in to a Modbus master instruction (at least for Micrologix and AutomationDirect CPUs) must be one higher - to write to the speed reference set the address to 48194.
 

Similar Topics

Power flex 527 Network based safety drive had faulty and alarm pop up SOS Code internal fault Unable to set or clear the fault manually or...
Replies
5
Views
115
Hi all. Would anyone happen to have the Modbus register datasheet for the Honeywell/EnergyICT EIMFlex Modular Meter v1.11 We've 40 of these that...
Replies
0
Views
64
I have an issue with Power Flex 525 during running processing, the VFD stopped suddenly while the PLC and VFD connection ok, VFD does not have any...
Replies
1
Views
123
I am trying motor startup with pf525 drive by using wizard start over ethernet communication but during direction test it's showing control error...
Replies
3
Views
184
i have a flashing yellow sts light. "Stop Asserted" message on one of my PF 753"s, but no bits set in parameter 961. The safety circuit tests...
Replies
1
Views
205
Back
Top Bottom