Has any one run into a problem where the Most significant and least signigicant words between 2 devices are different.

This seems to be my problem when writting a Long Int from the ML1500 to the Emerson Ei-203.

In my ML1500 I use a "CPW" to move my data from Longs into Intagers, swap the MS wors with the LS word, then send them off to the servo.

For my feedback from the servo I do the same but in the reverse direction.

This works great untill I have Negative Number, then the Index Distance I have sent my servo goes all waky, and the servo makes a very long index.

Note: the data type in the servo is definetly a Signed 32bit integer

Any help would be greatly appreciated.
 
Ok so I dug a little deeper.
Turnes out when I use the CPW function to turn the 1 long integer word into 2 integers, the CPW only writes to the first integer and not the second integer.

So because the Second words is All 0 at the bit level my servo distance is all wonky.

SO how do I move the Long into 2 ints and keep all the bits in both the MS Word and the LS word.

Going from 2 ints to 1 long seems to work flawlessly (hopefully by saying that I do not activate a curse)
 

Similar Topics

Hi all, PLC : Micrologix 1500 lrp HMI : Renu FP3070 TN I am a beginner in the plc world. I am trying to connect the renu hmi with ML1500 lrp in...
Replies
5
Views
725
Hello folks, Hope everyone is doing well. I am a beginner at working in analog signals with PLC Analog module: 1769-IF4 ( 4 analog inputs ) PLC...
Replies
9
Views
1,330
I have a Allen Bradely 1500 that has a cracked board. It still works but needs replaced (battery is no longer connected). To make migration easier...
Replies
10
Views
3,200
I inherited a system with the Micrologix 1500 talking to 8 VFDs using Modbus RTU protocol. One of the VFDs was replaced with a Toshiba VF AS1...
Replies
1
Views
1,178
Hello, I have the PLX setup and configured. Its seen and downloaded to. However my ML1500 does not communicate over it. The port (0) is used...
Replies
5
Views
1,627
Back
Top Bottom