I am looking at some S5 statement list programming involving an extended flag. I can't find the difference from a flag and a extended flag. Any help or a direction to find the answer would be helpful.
Thanks Mike
 
"Flags" usually means the "Merker" bits Mx.y.

Maybe you mean the extended datablocks, DX ?
These are like normal DBs. As far as I remember it is for when the normal number of DBs supported by a CPU is not enough.

Disclaimer: It is 20+ years since I had to work with S5 :)
 
If you mean S-flags, their use is restricted compared to M-flags.

As far as I can remember, the S-flags cannot be used as parameters on FB-calls (the bit length of the MC5-code does not 'fit').

I'll look for the manual ...

Kalle
 

Similar Topics

Good morning fellow sea captains and wizards, I am being asked to do the above and obtain 4 values from each slave, I know about the MRX and MWX...
Replies
20
Views
221
Hi everyone, I am an omron plc tec , lately I came across a siemens s7 200 cn plc . Can someone help me regarding the software required and...
Replies
26
Views
465
This is the first time I am working with Simatic Manager Step7 as I started my siemens journey with TIA which is pretty easy and do a lot of stuff...
Replies
3
Views
117
Hi, I have PLC S7-1200 and switch XC-208 and Iam trying to implement this SNMP library: SIOS I am not sure, what I am doing wrong, but there is...
Replies
3
Views
122
Hi all, i am the new controls guy at the plant and i have inherited a pc from the previous controls guy with Siemens tia portal version 16 and 17...
Replies
20
Views
731
Back
Top Bottom