How to change the displayed screen onto TP177micro from the PLC

Gromit

Member
Join Date
Jun 2006
Location
-
Posts
119
Hello,

How can I change the currently displayed screen onto a TP177micro Simatic panel from the PLC. I use WinCC flexible 2005.
Which word variable into the S7-200 should I change in order to change the displayed screen?

Regards
 
Whatever you like...Just create a tag within wincc called (say) 'Screen_Ctrl' using for instance VB0 and under EVENT set the Function to 'Change screen by number'...

One thing i found out is to set (under General) the Acquisition Mode to 'Cyclic Continuous' otherwise the screen seems to miss the request?

Hope this helps...
 
One thing i found out is to set (under General) the Acquisition Mode to 'Cyclic Continuous' otherwise the screen seems to miss the request?

If you don't change it to cyclic continuous then it only updates when its displayed on the current screen. Cyclic continuous updates the tag all the time at what ever rate you have setup default is 1 second.
 

Similar Topics

Hoping someone can give me some guidance or confirmation of what I need to do. We have a FactoryTalk SE program that I need to change the IP...
Replies
2
Views
80
Hey all, i have a panelview screen (image attached), with 4 items on it. Program 1, Program 2, ...3, ...4. The PLC i am using is a compactlogix...
Replies
5
Views
169
Greetings I have a problem, my system is the following: wincc v8.0 (demo), logo8.3, abb m2m analyzer. I created some pages to display the...
Replies
0
Views
61
We had one go down. we have a new one. Their emergency Number don't work. The Model is TLSA046AAH-330N01-007 A catalog says we need software TET...
Replies
2
Views
170
“The HMI files we cannot open—they were saved in V13—we do not have that—I cannot restore file –please have them save in V11 and send them back to...
Replies
4
Views
173
Back
Top Bottom