Comms question

KingPresident

Member
Join Date
Aug 2015
Location
Michigan
Posts
138
Setting up messaging/produce-consume tags between a couple plcs. Can I Raw socket the plant network between my 1768-L43s and my 1769-L30er? Or will I require two 1768-ENBT's?
 
The Ethernet Socket Interface is intended to be used when connecting Logix controllers to Ethernet devices which do not support the EtherNet/IP application protocol.

You definitely do not need Socket Interface to communicate between two Logix CPUs, either implicitly (Produce/Consume) or explicitly (Read/Write Messaging).

As to 'Raw socket' the two controllers to anything on the plant network, only the 1769-L30ER CPU has the capability to do so.

The older L43 CompactLogix will require a connected 1768-EWEB module carrying firmware 4.006 or later in order to acquire Socket Interface capability; the 1768-ENBT Ethernet bridge will not do.
 
どういたしまして (Doo itashimashite)...:D

Really, you could P/C/Msg all day long between any Logix 5000 controllers on the same ENet subnet (or CNet network) since....Ummm...The first Logix 5000 CPU came out....
 
Last edited:

Similar Topics

Question- I was given a Micrologix .RSS file and a .APA file communication is ethernet. I was asked to verify comms ethernet (which they...
Replies
0
Views
431
Good Morning! I need to monitor ethernet comms, between 2 Compact Logix PLC's. I have done this before with a simple pair of timers, toggling a...
Replies
7
Views
1,598
Hi I have an old Siemens S7-300 plc with a CPU313C. The firmware version is 2.0.12 so am presuming its an oldie. I have a model elevator...
Replies
5
Views
1,811
Hi Everyone. I’m using an Omron low end PLC, and I'm modifying an RS232 serial program, and I want to trigger from the RX receive flag and simply...
Replies
3
Views
1,775
Hi guys, hopefully someone here has a logical explanation for me on this one. We ran some Cat6 cable from a HMI (Proface) to a switch about 50...
Replies
3
Views
1,376
Back
Top Bottom