STI timed PIDs on SLC5/05 to Compactlogix migration
bigLee
Jun 2018
Florida
77
Hello,
I've done several migrations from SLC 5/05's to 5370 L33ER Compactlogix controllers.
I've just encountered my first PID instructions with STI timing parameters. Is this similar to a PID within a scheduled task in new controllers?
Do I need to make any special changes or will the conversion tool translate this fairly seamlessly? I know I'll have to verify the PID from the PCE warnings, but I'm just concerned about the PID executuion once converted.
They control several high output pumps. Any insight from any of the vets out there is as always appreciated.
Thanks,
Ben
You will want to be careful with the controller selection and tuning. I would expect the translator to correctly select the dependent gains equation, which will allow for direct copy of the reset time [minutes] and rate time [minutes]. The proportional gain will need some careful examination because in the SLC the instruction set reference implies that scaled error is used in the PID computation, whereas the PLC-5 and Logix processors are based on 0 to 100% scaling. It may be necessary to compensate for this if the SLC was not using default 0-16383 scaling for both the input and output. I find the SLC reference manual a bit confusing on this point, and it is especially important with the dependent gains form.
HI can somebody explain STI preferably with example thanks a lot
7,195
Hello, I recently started working at a place that uses Emerson/GE. They have installed some newer RSTI-EP remote I/O replacing the old genius...
172
Good day Programmers I have a RSTi-EP CPE100 Standalone Controller from Emerson as well as a STXMBE001 (MODBUS TCP/IP) as a Modbus communication...
636
Pulling my hair out again. I'm using RS Emulate 500 I have read everything I possibly can in the 1400 reference manual. My STI is working, but...
952
Hi all, Trying to set up a new positioner and require a password for a IMI STI STID8FT ?? Any suggestions as we cant get support until the...
2,105