Schneider TM221CE16R & SoMachine

If you use read/write blocks, then there is no need to select modbus mapping. M221 maps %M and %MW variables on behind automatically to modbus addresses.

Modbus mapping is for different configuration.


On master side you program write/read blocks according help files and block points with IDx number to partner PLC. (ID1 = slave 192.168.1.10).
You can have 16 different IDs on master side. (And slave IP addresses)


On slave side, you only need to give IP address and select enought %M and %MW variables to use.
(Default setting is that highest bit or word is highest uesd variable on program. On settings you can select that there is more variables, than you use on PLC program)
 
🍻 would be better (y)

If you have 1.5 Somachine, then you can also use IO scanner functionality for serial or communication blocks.
 
I have to get TM221M32TK - SL1 (Serial 1) to connect to their SCADA and SL2 - To HMI GTO 6310



i want to know how i can configure this? please direct me to the right way.



Thank You
 
I have to get TM221M32TK - SL1 (Serial 1) to connect to the SCADA and SL2 - To HMI GTO 6310



The data from the Tm221 port SL1 has to be collected at Mauritius, thats via network , is the module compatible for the purpose.

and which modbus is require rs485 or rs 232.

i want to know how i can configure this? please direct me to the right way.



Thank You
 

Similar Topics

Hello, I need to access the bits from the fire system control panel through RS-485. So, I used Read Var block to read from the panel...
Replies
0
Views
40
Hi Please I have zeilo smart relay #SR2A201BD but I don't have it's programming cable. Can I use any general usb/rs232 converter? Or need...
Replies
2
Views
79
Hello, Recently I was asked to analyze the logic of the air conditioning system in one of our departments. The PLC that controls this system is...
Replies
2
Views
122
I have an old PLC (circa 2007) consisting of Telemecanique/Modicon/Schneider Electric devices. The system has developed errors and unfortunately...
Replies
2
Views
177
Bisakah bapak untuk cara cepat mendownload data kerja dari komputer ke alat HMIG3U Schneider ? Terdiri atat apa saja ya dan bagaimana hubungan kan...
Replies
0
Views
52
Back
Top Bottom