I have a 1734-AENT configured in RSlogix 5000 with an IA4 module. I was expecting to see a controller tag something like FS1:1:I.Ch0Data, but I don't see any channel data anywhere. I just have FS1:1:I.0 - FS1:1:I.7.
Am I missing something or can somebody point me in the right direction? Thanks!
More specifically, the 1734-IA4 is a Point I/O four-point AC module. The "A" denotes the required supply voltage for the module. Not to be possibly confused with "A" denoting an Analog module.
That is if you are referring to "channel data" as being that of the Analog type? The example address "FS1:1:I.Ch0Data" would suggest as much?