Texas Instruments Series 305/Siemens question

Johnny T

Member
Join Date
Jul 2003
Location
Fife, Scotland
Posts
642
As Penelope Pitstop would say... HeeeeeeelllLLLLPPP!!!

I was given the job of replacing a Texas Instruments Series 305 PLC with a Siemens S312 series PLC.

So far... So good...

The Texas rack is as follows (from left to right):
24VDC Input card (8 inputs)
24VDC Output card (16 outputs)
Fast Response 305-01H card which has the following labels next to the LED's:
0 X4
1 S5
2 X6
3 S7
24VDC Input card (16 inputs)

I installed the Siemens modules and powered up but then discovered (to my horror) that it appears that the Texas Instruments modules are switching 0 volts and so the Inputs are getting 0 Volts instead of 24 !

So.. I've ordered two of the appropriate input modules from Siemens. I've also swapped the output card for a Relay Output card and wired it so it will switch 0 Volts.

My question is this:
Does anyone know how the Fast Response card works / what it does etc, or can anyone point me in the direction of any info on it.

Also, I've looked at the modules and there is nothing on them to indicate that the inputs are expecting 0 Volts. Is there any way to tell in the future whether a module is PNP or NPN ??

I'm back on site tomorrow so would appreciate a speedy response to this one...

I've also got a software question but will start a new topic with that one...

A big thanks (as ever) for any light you can shed on this...

Cheers

JT
 

Similar Topics

Texas Instruments PLC model 500 series; does any one knows were I can still purchase the software for uploading the program ? Ervin
Replies
1
Views
2,765
Instruments Series 500 Controller 530T-1104 Could anyone help!! I have a 3 Series 500 Controllers that require a routine battery change. The...
Replies
7
Views
5,480
I am trying to translate a program for a Texas Instruments Series 305 PLC into Siemens Step 7 and have come across a couple of things that puzzle...
Replies
8
Views
7,587
Hi everyone I have a customer who still has quite a large number of machines that is still being controlled by the old Texas 5TI sequencers. I am...
Replies
0
Views
2,033
TI CVU HMI database contains IAU/EAU/IAP/EAP after the PLC variable addresses ,for example:TCC1/IAP Anyone has idea what this means?
Replies
0
Views
1,299
Back
Top Bottom