Hey guys,
I need to have a boolean in Logix5000 that's always on. In other PLCs I've programmed (like GE, for example) there is a system tag that is always on. I'm not seeing anything like that in Logix5000. I was thinking I'd just get a coil on a rail with no contact in front of it, is that an acceptable way of doing things or is there a reason why that isn't best practice? Thanks!
I need to have a boolean in Logix5000 that's always on. In other PLCs I've programmed (like GE, for example) there is a system tag that is always on. I'm not seeing anything like that in Logix5000. I was thinking I'd just get a coil on a rail with no contact in front of it, is that an acceptable way of doing things or is there a reason why that isn't best practice? Thanks!