Panelview 300

Exposition (and an example of why we always ask for the exact PanelView part number):

Code:
2711   PanelView Standard
K      Keypad
3      3" LCD Screen
A      Monochrome.  Originally meant "Amber".
2      Data Highway 485 with DH485 modular plugs (not RS-232, no printer port)
L1     DC 24V power


If this is connected to an SLC-5/03, it's very probably going to use the dedicated-purpose Data Highway 485 cable from the "AMP jack" on the PanelView to the RJ-45 network jack (DH485) on the SLC-5/03 CPU.

Those came in a handful of premade lengths, and 1747-C20 is twenty feet long.

RA didn't make longer pre-made cables for that specific connection because the PanelView's isolated network port actually gets 24V DC power through that cable from the SLC-5/03's network port, so the voltage drop through those small conductors limits you to about 20 feet.

If you used separately-powered network isolators like the 1747-AIC or the 1761-NET-AIC, you could run the full 4000 feet or so of trunk cable length supported by DH485 network signals.
 

Similar Topics

I am having pvc300 with me. I created my new program in ccw. The issue is that after clicking discover in ccw my hmi is not showing up there. Any...
Replies
0
Views
144
merry christmas and happy new year i have a click c0-00dr-d and allen bradley 2711c-t3m. can the panelview talk to the click plc via modbus...
Replies
1
Views
213
Is this the clock battery flat? Does anyone know how to remove the back of the PV 300 micro. Is it possible to replace this battery. AB says it's...
Replies
2
Views
1,152
Hey Guys I am trying to figure out the correct cable to use to connect from my laptop to this Panelview using panelbuilder32. I was sure I had...
Replies
5
Views
2,040
I need to utilize the program of Panelview 300 standard into Panelview 7 plus. Can anyone plzz help in this regard??
Replies
2
Views
1,400
Back
Top Bottom