Hello everyone,

I'm new to the forum and I've never work with analog sensors before.

How do I wire up 3-wire ultrasonic analog sensor to Allen Bradley PLC?
I don't understand wiring diagrams of the PLC.

PLC - CompactLogix 5370 L2 / pn: 1769-L24ER-QBFC1B
link: http://literature.rockwellautomation...m021_-en-p.pdf
Analog sensor - pn: UK1A-E2-0A
link: https://cdn.automationdirect.com/sta...mmultrauk1.pdf
  Reply With Quote
Old January 11th, 2018, 04:31 PM   #2
Webhead
Member
United States

Webhead is offline
 
Webhead's Avatar
 
Join Date: Jun 2005
Location: Central Florida
Posts: 120
If I'm reading the cutsheet correctly, Brown goes to +24VDC, blue to (-) terminal on plc input and black to (+) terminal on PLC. If that doesn't get you where you want to be let us know.
__________________

There are 10 kinds of people in this world. Those that understand binary and those that don't.

  Reply With Quote
Old January 11th, 2018, 04:42 PM   #3
mikeecbr
Member
United States

mikeecbr is offline
 
Join Date: Jan 2018
Location: Chicago
Posts: 2
Quote:
Originally Posted by Webhead View Post
If I'm reading the cutsheet correctly, Brown goes to +24VDC, blue to (-) terminal on plc input and black to (+) terminal on PLC. If that doesn't get you where you want to be let us know.
Hi Webhead,

I don't quiet understand what you mean by (-) terminal on plc input and black to (+) terminal on PLC. I don't know how to wire up whole analog implemented i/o module. Please see attached.
Attached Images
File Type: jpg Analog io.jpg (52.9 KB, 73 views)
  Reply With Quote
Old January 11th, 2018, 10:02 PM   #4
Brandon_K
Member
United States

Brandon_K is offline
 
Join Date: Mar 2016
Location: Pittsburgh, PA
Posts: 139
Assuming you have no other analog devices connected;

You want to use diagram 3 on the ultrasonic sensor.

Brown +24v from power supply
Blue 0v from power supply
Black "I in 0+" on the PLC

You'll need to also have a short jumper on "I in 0+" and "V in 0+" to bond them. Lastly, you'll need to run a connection from the 0v connected to the blue wire of your sensor to to "V/I in 0-" on your sensor. This is on the bottom of page 184 in the manual you linked to.

Basically blue and brown on your sensor are to power the sensor. Black is your +mA output from the sensor. But it's a 3 wire sensor, so the 0v (blue) does "double duty" both powering the sensor as well as providing a reference to the controller.
Attached Images
File Type: jpg allenbradley.jpg (35.4 KB, 58 views)
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Analog output (ABB AC500 PLC ) scaling muza1988 LIVE PLC Questions And Answers 3 March 8th, 2015 12:05 PM
Rs logix 5000 varunmahendran91 LIVE PLC Questions And Answers 4 October 6th, 2014 01:26 PM
analog control using plc (urgent request please) osama_love_natch LIVE PLC Questions And Answers 1 June 5th, 2014 08:13 AM
Control Valve through Analog Input/Output - Beckhoff PLC tech007 LIVE PLC Questions And Answers 3 September 26th, 2011 05:42 PM
PLC Analog IO andydas LIVE PLC Questions And Answers 3 October 3rd, 2003 05:49 PM


All times are GMT -5. The time now is 10:05 PM.


.