Question about star-delta control circuit diagram

Wye delta

K1T ( n.c.) is in wrong location. It should be on 2nd rung to open k1 resulting in k3 being energized by k1 interlock . Basically transition from wye to delta connection.
 
K1T ( n.c.) is in wrong location. It should be on 2nd rung to open k1 resulting in k3 being energized by k1 interlock . Basically transition from wye to delta connection.
welcome to the site
Can you please check the date of the last post

2009 is very old
 
Hi Shilpesh
From your circuit diagram,K1 is for STAR connection.For Star delta Starter,The first sequence after you press ON push button is K1 MUST energize first before K2.Why? because if K2 energize first before K1 it can cause the spark and can damage the contactor. The Key point for star connection is to start the motor in 240 Volt to reduce high in rush ampere and build a torque..after a motor achieve 80% running..it switch to Delta.It mean the motor running with full capacity ( 415 volt )..For more detail,please read some post about star delta starter below :-

http://www.electricneutron.com/electric-motor/star-delta-motor-connection/
http://www.electricneutron.com/motor-control/star-delta-starter/
 
Hi Shilpesh
From your circuit diagram,K1 is for STAR connection.For Star delta Starter,The first sequence after you press ON push button is K1 MUST energize first before K2.Why? because if K2 energize first before K1 it can cause the spark and can damage the contactor. The Key point for star connection is to start the motor in 240 Volt to reduce high in rush ampere and build a torque..after a motor achieve 80% running..it switch to Delta.It mean the motor running with full capacity ( 415 volt )..For more detail,please read some post about star delta starter below :-

http://www.electricneutron.com/electric-motor/star-delta-motor-connection/
http://www.electricneutron.com/motor-control/star-delta-starter/

welcome to the site
It is great to see new input from new members.
but
please check the original post date
this is from 2007 (5 years old);)
 

Similar Topics

Found that a trouble some pumps that kept causing overcurrent faults on the VFDs were wired in star instead of delta configuration. In star...
Replies
6
Views
2,603
I have an HMI 2711R - T4T Series B, and I want to know which PLCs, besides Micro 820, can communicate with it.
Replies
2
Views
53
HI i would like to know how to get a variable that will store the amount of times a program has been executed. The issue is I have 3 DBs for 1 FB...
Replies
2
Views
58
I'm working with a project that contains some routines in ST but mostly in ladder. Am I correct in assuming this 'rung': DB1001DO._01AV55_OPEN :=...
Replies
4
Views
95
Is there a way to reset the count on the RS Logix BackUp?? XXXXX PROGRAM IN PROGRESS_BAK445.RSS XXXXX PROGRAM IN PROGRESS_BAK446.RSS XXXXX...
Replies
8
Views
247
Back
Top Bottom