Versamax CPU001 RS485 RTU
alencknovi
Jun 2019
Croatia
I want to communicate with versamax CPU001 on port 2 with rtu slave.
I build up a cable two wire as per instruction here:(typical 2 wire)
http://technolink.spb.ru/downloads/GE_Intelligent_Platforms_PROFICY/documents/Modbus_GFK2220C.pdf
And have 485 to ethernet converter that has 2 wire connection.
On controller i have set up port RTU only 19600, 2 wire
I am trying to send commands but i get no response from plc at all.
Dont know what where to look for mistake or should i have something in ladder to initiate communication when using plc as slave?
Make sure your polarity is correct between the PLC and your converter. GE's pin labeling can be a bit confusing. "A" on the GE side is minus. "B" is plus.
You don't need any ladder logic in the PLC when the port is set up as a slave.
Temporary lost power to plant .. One of the processor fault when power were restored.. I cleared fault, but all of the Inputs to the I/O module...
1,674
egcp-2 from woodward has rs422 port which can be used for modbus communication and gefanuc versamax plc has rs485 port which supports modbus...
3,167
I have one GE Fanuc IC200PNS002-AC Versamax Network Interface Module and the fault red light is blinking and i have checked in manual it is...
214
Hi, The VersaMax PLC suddenly stop running (no LED on run function) so I'm trying to upload the program. The HMI connected to it says "Host...
132
I do have a problem with a GE Versamax micro PLC. By going online (on Port 1) the "OK led" goes down. Power led stays On Port 2 no reaction at...
389