A-B PanelView7 Standard doesn't read processor tags
Hi all,
I've trouble with communication between PV7 and processor values.
A network of a IO rack (with 1747-AENTRs) and 3 PanelView7 standars is a ring. All racks and PV7s are connected to ETAPF2s. Network works properlly. First PV7 works correctlly also. But a second one has trouble with connection to him proccesor and read/write data.
If I check application in runtime on eng station, everything work, can see values, control valves... But If I download application to PV7 and browse display with values, than see DIAGNOSTICs PANEL:
[FactoryTalk]: The Item is no longer available: [shortcut]tag
All tags on HMI screens are online values from processor.
FT View ME is v 10.00.01, firmware in PV7 also v10. Rev. in CompactLogixes is 30.11
A HMI project of second one is copy of first one. And first one is working properlly. Shortcut for first processor is: [1], for second one is: [2]. Both PV7 are communicate with different processors.
Do you have any idea or experience with this?
My imagination is over.
Unread August 13th, 2019, 01:24 PM   #2
scarince
United States
scarince is offline
I'm not exactly clear on your setup because you talk about 3 PV7's and two different logix plc's..... but have you ruled out configuration problems? Can you ping the PV7 that isn't working? Could you have duplicate IP addresses?
Unread August 13th, 2019, 01:42 PM   #3
Operaghost
United States
Operaghost is offline
Operaghost's Avatar
Generally if it works on your engineering station but does not work on the PanelView terminal then the problem lies with RSLinx Enterprise (now called FactoryTalk Linx in newer versions).
In the Communications Setup there are two tabs. Design handles the communications so that your computer can act like the PV and talk with the PLC. The Runtime tab is where you configure how the PanelView talks to the PLC. It sounds like the Design tab was configured (because it works on engineering station) but the Runtime was not (because the PV isn't working)
Open the application in FactoryTalk Studio and in the RSLinx Enterprise Communications Setup there is a button to copy the Design configuration to the Target tab. Do that, apply and click OK. Then create a new runtine.
OG
Unread August 13th, 2019, 02:06 PM   #4
Tom350
Czech_Republic
Tom350 is offline
Scarince:
All IP addresses are unique. I can ping all IO racks, processors, PV7's. IO network works properlly.
In ring network are IO racks and 3pcs PV7's, ring is connected to Stratix5700. Processor are star to Stratix5700.
Each PV7 should communicat with his processor. All network contain 12 processors, for each processor 12 IO rack. And 3 processor have PV7's. except IO racks.
Operaghost:
Design and RUntime are setuped also. In network is 1PV, that works in excellent condition. This second (and third also) do this fault.
Unread August 13th, 2019, 02:41 PM   #5
mike3475
United States
mike3475 is offline
did you try to use USB flash copy .mer file,then insert to second PV7 and load it?
Unread August 13th, 2019, 02:45 PM   #6
Tom350
Czech_Republic
Tom350 is offline
mike: not yet. Only download cross ethernet connection. Will try copy from USB flash.
Unread August 13th, 2019, 02:54 PM   #7
mike3475
United States
mike3475 is offline
go to second PV7 panel configuration mode to check .mer file, maybe you load wrong file before.
Unread August 13th, 2019, 03:07 PM   #8
Tom350
Czech_Republic
Tom350 is offline
Mike: This I checked. Tryed make blank FT project, with setuped communication and 1 value on HMI screen. And was same.
Unread August 13th, 2019, 06:06 PM   #9
mike3475
United States
mike3475 is offline
http://www.plctalk.net/qanda/showthread.php?t=69514
Unread August 13th, 2019, 06:23 PM   #10
Ken Roach
United States
Ken Roach is online now
Ken Roach's Avatar
If your sample application doesn't work, then the problem is very likely to be in your communication configuration.
Either post the Archive file or some screenshots of your destination tab in FactoryTalk Linx.
Unread August 14th, 2019, 10:48 AM   #11
James Mcquade
United States
James Mcquade is offline
if you have multiple pv terminals on the same network, each pv terminal MUST have its own set of display control registers in the plc.
james
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
S7-1200 SCL - read whole I/O port PartTimePlcProg LIVE PLC Questions And Answers 11 February 17th, 2016 12:02 PM
Trying to understand safety PLC's (specifically Siemens) Jieve LIVE PLC Questions And Answers 3 June 24th, 2014 09:27 AM
WinCC Continuous CSV read SYED.ABIDI LIVE PLC Questions And Answers 9 March 24th, 2013 12:05 AM
WinCC Continuous CSV read SYED.ABIDI LIVE PLC Questions And Answers 0 March 20th, 2013 03:43 AM
i cannot read from the DELTA DVP28SV PLC registers? nura91 LIVE PLC Questions And Answers 1 July 10th, 2012 07:05 AM