i am doing a project with a conveyor and sorting system using the Mirco 850 PLC and micro hmi for the control system of the conveyor.



I also have on a separate network a software application using Delphi programming language. Basically just for operator input and indication from weighing scales.



I wanted to add a sensor/scanner to the computer where it can pick up a counting pulse and display it on my computer program.



Is there a way to count a pulse from the PLC or device and count perhaps via rs232 or ethernet to my computer software?


thank you
 
The Plc(Micro850) can send MODBUS data out using RTU/TCP, so if the computer program can capture Modbus Data you could do anything you want with that data.
 
I've used a python library in the past to extract inputs and outputs from a PLC. This can also be achieved with an OPC server software; for example: Ignition.
 
Thank you @damica1 for the reply.



How would i do that, do i need an card or interface in the PC to read that data?

Depending on which protocol you use? If you use Modbus/Tcp and as long as the computer had an ethernet port all you need to do is find/download a Modbus Client that can provide some type of Capture/Export.

Now if you are the one writing the computer software you should be able to embed all the needed function into the PC software.
 
I think the Modbus options sounds the most promising.


If it does not pan out, somebody already mentioned Ignition (10kUSD and up); there is also AdvanceHMI, which I have not yet tried but seems to do this kind of thing well, in YouTube videos at least.
 
The only problem of counting pulses sent from a PLC via Coms will be if the pulse i.e. bit you are reading is faster than can be captured via you PC program. In that case, it would be better to count the pieces in the PLC and read the value as an integer, you could then send a bit back to the PLC when you need to reset the count. In other words, let the PLC do the work, coms is a tricky subject, to make it more efficient sending information from PC to PLC will normally only be done on change releasing some coms time to for the PC to read data from the PLC as fast as possible, another consideration is to make data read or sent to be contiguous so that it reduces the number of transactions, reading values from areas of memory that are not contiguous means you have to read the ones in-between or make more transactions.
 

Similar Topics

Hello I need to message read the entire 16 channel raw analog inputs from a 1769-L33ER Compact Logic controller to another 1769-L33ER Compact...
Replies
8
Views
240
Good morning guys; Im new at AB plc, and i just need help about a table or a list called something like "exchange data table" in French it is...
Replies
4
Views
767
What he have is a HMI2GO unit ( KTP900F) and we use a safety relay to trigger our e-stops. What the tech wants to do is guard against e-Stop on...
Replies
2
Views
1,856
Most PLCs are 24v for digital logic, will a Digital input card detect a 12v (automotive) signal as a 1 Looking to do some work on a...
Replies
11
Views
4,285
Hello PLCs.net! I have a kinetix 5500 drive connected to a gantry, I was wondering if there is a way to do active homing using a PLC tag? At this...
Replies
6
Views
3,048
Back
Top Bottom