Easybuilder pro

Miguel.itlac

Member
Join Date
Apr 2020
Location
Mexico
Posts
4
Hello everyone

Im Newbie to Easybuilder and im designing and HMI application where I gotta display a warning message in a pop up window everytime there is a fault in the drive, i have 24 different faults and 2 drives, so it comes to 48 windows, alot right?. I have more experience with Factory talk and ive used only 1 window for repetitive data with the help of macros to change just the data.
I wonder if anyone has done that before with easybuilder
And if so, it could be of help
Thanks in advance.
 
This is just another solution if it was me, I would still only have a single window.

Example: the Schneider 600/900 series drives present their error code in a "Word" format

So I would create a "Table-in the HMI" with all the error codes for your drive.
0=No Error
1=Dry Run Error
2=Over Current
3=Over Voltage
4=Phase Loss
5=Motor Short Circuit
And continue on with the drives complete error code. Then just set up a Fault trigger so when drive faults it will read the error word to get the actual error and display that in a box for Drive 1 and or drive 2.

As I said just another solution.
I do this with the Schneider Altivar 600/900 and Modbus Tcp. I would not know how to do it any other way.
 
Last edited:
Thank you very much to everyone for your answers, i didnt have another quick option so i actually did what Damica1 said

Greetings,
Miguel.
 

Similar Topics

I have EB Pro installed on windows 11, I can open an existing project and edit but when I got to parameters tab and open page I get the hourglass...
Replies
0
Views
52
Hi, I would like to know if it is possible to modify the properties of an object via a macro? For example I have a value of 100, via conditions...
Replies
0
Views
865
Hi, I'm an intern student engineer and I'm tasked with creating a HMI for a control system in EBPro. I need to make an object (motor) which has...
Replies
5
Views
1,759
I am banging my head trying to get EB Pro to convert simple math expressions. Ex: 1 Pump conversion coming from a SCP instruction O0 1.1 value...
Replies
2
Views
1,859
Hello folks, I am working on an HMI application in EasyBuilder Pro using the software with the Simulation mode as an MQTT Edge Gateway. This...
Replies
4
Views
2,069
Back
Top Bottom