Recently encountered the F122 fault on the PF525 VFD and curious what could be the reasons for it?
The attached are the instructions to clear it, but not reasons why.
Thanks.
Interesting, I just had this same fault pop up too. Pretty much a brand new drive too, maybe some defective units are out there. I should say, we did find a bolt in the pump...:confused:
The KB basically just say to re seat the IO module. I think I had this fault on a drive a few years ago. Had the operator clear it and keep going and I don’t think it’s ever showed it’s face again.
On the 525, there is a Control Module and a Power Module that snap together. There is a multi-pin connector that allows the Control Module to communicate to the Power Module and that can become a point of connection failure under vibration or corrosion (or both). If the Control Module goes bad, you don't need to replace the entire drive, just the Control Module. All Control Modules are the same regardless of size of the drive, when you plug it in, the PM tells the CM what it is. You will get an error that you have to clear. But try just reseatting it first...
https://www.youtube.com/watch?v=BgornT7mv8s
I seem to be on here often lately but cant find specifics about my situation I am trying to control the drive using both ethernet and analog(for...
747
When E300 powered off, the ethernet device tag data stayed at last know state, for example, fault bit is still Off, ready bit is still ON, status...
1,006
Hello all, New to this site - I am adding a new conveyor and using a powerflex 525, though the rest of the drives operating this line are...
1,282
I have a (*) PowerFlex 525 being supplied with 400VAC, 60 cycle, 3-phase. This is not a type-o, this is accurate. Now, the drive clearly states...
1,179
Has anyone had any success using a PanelView Plus to directly control a PF525 over ethernet, I tried to use the file provided with TechNote...
1,060