I have issue of ground fault on the drive powerflex 755 110kw , i check motor terminals, megger it found that greater than 220 MOHM resistance in all winding to earth , that ground fault followed by HW overcurrent fault occur once in a while in day during running , sometimes it reset through drive HMI red button sometimes it not reset with it then i have recycle the power then it clears ,
what may be the issue?
also
Can I run powerflex 755 drive without motor load for 1 day ? so that if fault comes then we sure that its from drive itself , is there any problem with drive if you run drive without load for 1 day ?
I really appreciate your help
 
Sir ,
Is it good to run drive without load for long period of time . so that if problem coming from drive we are sure of it
 

Similar Topics

So I have a sort of unique situation where I'm wanting to run a PF755 from the IO and over ethernet. Of course, this comes with it's own set of...
Replies
9
Views
172
Hi I was wondering I need to update the firmware of a 755 inverter does the drive hold the program on the drive and just updates the firmware or...
Replies
5
Views
149
So I'm replacing a terminal block on the inverter board for a 755. I'm wondering if anyone knows what conformal coating would be best? I'm not...
Replies
1
Views
114
Hello guys, I am new to this forum and have some problems with my PowerFlex755 EENET frequency inverter. I want to do a point to point...
Replies
9
Views
379
Powerflex 755, running 2 weeks, and faulting with code 17 input phase loss.
Replies
3
Views
209
Back
Top Bottom