panic mode
Member
I have to deal with several machines that have S7-317F-2PN/DP processor.
Each panel has programming port on main cabinet with access to both Profinet and Profibus.
Devices on Profibus include CPU, small HMI (TP177B) and one or more CU320 (Sinamics S120).
There is also another HMI (main) which is on Profinet.
I have cable and CP5512 but I would rather just stay on Profinet. This is not a problem
when talking to CPU or servos (PG/PC pass through) but I can't connect to that
little TP177 HMI using passthrough.
Is there a way to set this up so everything can be accessed using just profinet?