TIA Portal and SFB52/53

Michal_dk

Member
Join Date
Oct 2007
Location
Vejen
Posts
153
Has anyone here had success with reading or writing parameters directly to a device using the SFB 52 or 53 blocks in TIA portal?

My problem seems to be in the address, if I set up a system in S7 Manager and a 300 CPU I have no problem. I use the "Diagnostic Address" of the device as the address on the SFB and communication works.

On the TIA portal I can't find the "Diagnostic Address" But I have the "HW Identifier", but using this I get an error everytime I activate the SFB.

I have tried searching the web but have until now come up short on an example that involved TIA.

I have TIA 11 and TIA 12 at my disposal.
 
Hmm, it would seem that the HW Identifier IS the address to use, but I get a status Word like this:
C089_3A00

C0 means "No DPV1 protocol element is used", but what does it really mean?

I'm using PPO type 5, so I think I'm using the right communication type?

Oh, and SFB 52/53 is RDREC and WRREC
 
Last edited:

Similar Topics

Hi! Is it possible to open the project I'm creating on a latest version? I'm working on TIA Portal V19, but the customer needs it on v18.
Replies
9
Views
226
Hi everyone I want to use a vm to run tia portal v13 to v15 What would you suggest, Windows an specification for each portal . Thanks will...
Replies
4
Views
113
Hi PLC people, think about this scenario: The PLC is somehow connected to the same network with the facilities` network. Then someone connects to...
Replies
2
Views
144
Hello, good morning, I have been having two problems with the Tia Portal software. The first is that I have installed it on my computer and...
Replies
5
Views
229
Hello all! So I have one project with a S7-1214 and a MTP1500 "Project1" and one project with another S7-1214 "Project2". Both of these PLC:s need...
Replies
6
Views
163
Back
Top Bottom