Best i/o for the buck?
ganutenator
May 2002
kansas
1,440
Looking for distributed i/o for an M340. Anything that talks modbus tcp.
All discrete i/o.
We are currently paying $7 per input, and $8.50 per output.
recommendations?
Opto22 Snapio. Modbus TCP and Ethernet/IP
You'd have to figure out price/pt once you figure out how many you need.
opto22.com
Automation Direct has some slice IO (probably made by either Wago or Beckhoff).
https://www.automationdirect.com/adc/Shopping/Catalog/Field_I-z-O/Protos_X_I-z-O
Automation Direct also has terminaotr IO.
https://www.automationdirect.com/adc/Shopping/Catalog/Field_I-z-O/Terminator_I-z-O
Wago, Beckhoff, Pheonix, etc just a few that has them.
the automation direct link doubles the price per i/o point.
Check out Omron- super nice slice I/O for pennies. Not 100% sure about modbus, but it can probably do it.
Omron uses Ethernet IP not Modbus. In Oz the input block is about $60 for 16 inputs and the same for outputs. Then there is the coupler but it takes heaps of I/O.
If you manage to negotiate good discounts with Beckhoff, you would be nicely surprised. Even at their list prices, it is about $5.40 for a discrete input and $5.90 for a discrete output. This is for 16-point 24V PNP EL series terminals.
I agree with this. It is very hard to beat Beckhoff. The quality is good as well.
Have succesfully used weidmuller remote io. But think they are also made by another company as it looks exactly like GE remote io. Used a m340 with noe and ioscanning
Have you thought about using AD's Click just as I/O? Might be worth it for the $/point...
The 16-pt src/snk input card would be ~$3.06 per point (IO card only)
The 16-pt src -or- snk output card would be ~$2.81 per point (IO card only)
The cost of the cpu would increase the price per IO point somewhat - depending on your selected cpu.
The CLICK cpu supports 8 expansion modules MAX!
Compactlogix controller, program has 28 conveyors that use TON's to start the conveyors. The TT sounds a warning horn during start and the DN...
485
I have S7 1512C controler for controlling 48 PID temperature loop, the output is PWM. Please I need the best, most efficient way to write the...
600
I am going to need to use HART multi-drop in order to handle a series of Vega Radar units. There are a lot of options and I'm wondering what...
253
Out of interest, I'd like some thoughts on what would be considered best practice with regards to a 2-position turntable control scheme (see...
17
1,131
Hello colleagues Anybody knows, what could be the best or a better option to bring with you when you are in service at factory to connect via...
261