Let me Clarify /prove my position in regards to proper conductor sizing.
"Conductors (motor or otherwise) have to be able to carry the current passed by the next upstream short-circuit device. That is a basic code rule and supercedes your erroneous belief in a "125% of FLA" rule that simply does not exist."
The NEC clearly does clearly specify 125% of FLA for the sizing of motor conductors.
Article 430 of the NEC cover motor circuits. (read section 430.1 scope). Conductor sizing is addressed in 430.6 and in part II (430.21 to 430.29)
Article 430.21 General state "The provisions of Articles 250, 300, and 310 shall NOT apply to conductors that form an integral part of equipment, such as motors, motor controllers, motor control centers, or other factory-assembled control equipment"
Article 430.22 Single Motor states "Conductors that supply a single motor used in a continuous duty application shall have an ampacity of not less than 125 percent of the motor full-load current rating, as determined by 430.6(A)(1)"
Article 430.6 states "The size of conductors supplying equipment covered by Article 430 shall be selected from allowable ampacity tables in accordance with 310.15(b) or calculated in accordance with 310.15(c)"
"You cannot legally (by the NEC) use a 300 Amp (no 310 available) inverse-time breaker to supply a 1/0 wire. Instead you would have to raise your wire size to 350 kcm."
The NEC clearly does allow the use of a 300 Amp inverse time breaker to supply a 1/0 wire, in a motor branch circuit. (it must be a motor branch circuit falling under the scope of article 430
Article 430 Part 4 covers Motor branch-circuit short-circuit & ground-fault protection
430.51 General states Part IV specifies devices intended to protect the motor branch-circuit conductors, the motor apparatus, and the motor against over-current due to short circuits or ground faults. These rules add to or amend the provisions of Article 240.
430.52 states that you use table 430.52 to size the motor branch-circuit short circuit protection
Table 430.52 shows that the maximum breaker size for an Inverse Time Breaker is 250%.
(note: Exception No 1 allows you to go to the next larger size breaker if there is not a standard size breaker that is 250%)
Articles 210 and/or 240 do not over-ride section 430 (in motor branch circuits)
Article 210.1 Scope states "This article cover branch circuits EXCEPT for branch circuits that supply only motor loads, which are covered in Article 430
Article 240.3 has a table 240.3 of equipment type and NEC Articles and tell you to use those articles for sizing conductor protection for those equipment types . The table calls out Article 430 for "Motors, motor circuits, & controllers"
"Oh, boy! There are a lot of mis-sized motor conductors out there. They will work okay, everybody fat, dumb, and happy - until someone cuts the wires with a forklift or crane or some other way. Then those too-small #1/0 wires will smoke, burn, flame up, and set the building on fire long before the 300 Amp breaker even thinks of tripping. I hope there are good smoke detectors"
With the 1/0 wires in this example the breaker will trip (or the O/L will trip if it is a low A fault) before the wires melt or vaporize (assuming the Short circuit withstand of the breaker and O/L is greater than the available short circuit current at that breaker, but you may have an even bigger problem with 350MCM in that case)
"NEC Handbook Article 430.22 note:"Motor nameplate full-load current is not to be used to size branch-circuit conductors."
You left out the sentence just before this one in this paragraph which completely changes the meaning. "The ampacity of the motor branch-circuit conductors is based on the full-load current rating provided in Tables 430.248 through 430.250."
Those tables state that you need to use 124A as the FLA. 124 is what we have been using in our example as FLA
"That is plain language in a NEC note that was written to kill the very belief that many now hold. Motor conductors must be no SMALLER than 125% of motor FLA, but in many cases they will have to be much LARGER than 125% of FLA to meet other requirements in the National Electrical Code (to carry the current passed by the motor branch-circuit device).”
This language is not in the NEC. The NEC states the opposite! However, you often need to increase conductor sizes based several reasons such as ambient temperature, number of conductors in a conduit or raceway, under ground feeds, conduits/conductors exposed to sunlight etc. (see section 310.15 for the de-rates). But the size of the breaker is not one of them when you are dealing with Article 430 motor branch circuits.
Over-sizing conductors is not a bad thing it is just not very practical. In my last big job we spent 1.2MUSD on copper (cable & wire)(the cost of wire & cable boils down to copper cost on big mill orders). 350MCM contains 3.3 times more copper than 1/0. If we oversized everything by 330% our cost for copper would have been almost 4.0 MUSD. You would never win any contract if your cost are 3.3 times higher than your competitors.