Hi guys

i'm newbe to FTV Studio and so i ask again your help! Two questions; the first: on plc i have an array for the alarms messages tag name = ALM type BOOL[1024[. Is better write 1024 alarm tags on FTV Studio or try to copy (on PLC) ALM bits array to DINT array and then use the DINT variables on FTV? If the second way is the best solution, what is the sintax on FTV --> alarm Setup --> Triggers for understand what bit is set (i.e. ALAM_DINT[0] && 2#1 for the bit zero ad so on ....)?

Second question: i need to manage two separate message category: alarms and service messages (for maintenance). Is possible make 2 differnt list for each category (like Alarm list object but also for service messages).

Thank you so much.
 
question 1.DINT's would be best. It would give you 32 triggers instead of 1024.

set trigger type to Bits. PLC Dint tags 0-31 will match up to Alarm tags 1-32. if DINT = 0 then no alarms would be active.

Your message file can use copy paste using excel. If description of alarms are already in PLC then export tags and copy from excel to message file.

The Message File is basically a spread sheet. Select a row and copy and paste in excel and you will see the format used by FTV.

alarm messages.PNG


question 2. Yes. go to properties of alarm screen open Alarm Tab, at the bottom you'll see a filter option. pick the triggers you want to display for that alarm screen. Triggers must be created first. Then you can use the radio button and just check the boxes.

alarm filter.PNG
 

Similar Topics

Hello everyone, I am currently working on a project that uses a Rockwell L33ER controller and the FTV Studio V13 as Supervisory computer...
Replies
0
Views
84
Hi all, I have FTV v13 installed on my VM. I made an ME application and exported it in v11, as that's the version being used on the Panelviews at...
Replies
3
Views
366
Hello Friends, I want to log FTV Studio SE alarms and event data into a oracle 12c database and as i checked the by default windows in FTAE...
Replies
2
Views
809
Just "upgraded" from v12 to v13. I've noticed that the diagnostic list messages are not nearly as descriptive. In the past, I'd get something...
Replies
0
Views
582
When I create a line in FTV Studio ME (v13 CPR9 SR13 - Patch 17 Build 413) and try to change the line style to anything but "Solid" it just...
Replies
6
Views
1,226
Back
Top Bottom