I am creating a control system to monitor several liquid inputs for a washing system. The inputs are to include several discrete IO, conductivity and temperature. I can manage most issues dealing with the programming, but my experience with analog is very limited. Actually I have no idea where to begin other than reading what I can on this website. I have read the SLC instruction manual dealing with Analog inputs and how one can configure the modules within the program, but I will be using a ML1100 (1763-L16AWA) and the manual is not as descriptive (no programming examples). I will be adding the 4 option modules in the following configuration.



Slot 1-- 1762-IA8 input module

Slot 2-- 1762-OA8 output module

Slot 3-- 1762-IF4 analog input module

Slot 4-- 1762-IF4 analog input module



During my reading on this site I have discovered that the ML1100 analog input cards have a configuration screen which can be accessed through the IO Configuration in the explorer window. Once here I can double click on the Analog module and get to a screen with 3 tabs (expansion general config. Analog input config. and generic extra data config). From this point I no longer have any idea of what to do.



Any programming or configuration ideas would be greatly appreciated.



Ken

 
First set dip switches for input type current or voltage (see page 8 of manual) default is current.

CardSetup.jpg


Raw input data values for card in slot three are in address ( see page 14 of manual)
I:3.0 channel one
I:3.1 channel two
I:3.2 channel three
I:3.3 Channel four
Same follow for card in slot four addresses will be I:4.0,1,2,3

I configured the card for 4 to 20ma and a data format of Scaled for PID this
configuration will give the following values in the input words.
4 ma= 0
20 ma= 16383
see PDF for data format values.

See sample program for scaling raw data to engineering units. (your scaling will vary of course)

Card Manual:
http://literature.rockwellautomation.com/idc/groups/literature/documents/in/1762-in012_-en-p.pdf
 
Last edited:
Thanks Mickey

Mickey,

Thanks for your response. This gets me on my way.

I could not open the logix file (new1100), but you gave me enough information to get started.

Thanks again
Ken
 
kbradray said:
Mickey,

Thanks for your response. This gets me on my way.

I could not open the logix file (new1100), but you gave me enough information to get started.

Thanks again
Ken

Maybe a ver. issue (I have ver 7.20 cpr7) as to why you can't open it? below is a PDF of scale example.
 
Going

Thanks again Mickey

I am rolling right along now thanks to your help.

This is really one of the first integrations from scratch that I have done. I have done several modifications to existing programs for add ons, but none from scratch. Sometimes I just need a nudge in the right direction to get the ball rolling.

thanks again
Ken
 
Be warned here (I ran into this a few weeks ago). A couple of the analog input cards for the micrologix plcs have dip switches on the boards that you need to access through the air vents with a small screwdriver to toggle the circuitry between current and voltage. You must do this as well as configure it through software or it will not behave correctly.
 

Similar Topics

Just asking for clarification here, but from my research all I need is a 500 ohm resistor across the AI and the common? Heres my schematic. I...
Replies
5
Views
2,546
Hardware: Micrologix 1100 & 1762-IF4 Analog Input Module Problem: I have one 4-20mA transmitter hooked up to I1:0, I am monitoring the current...
Replies
12
Views
3,359
Please can anybody recommend a way of measuring a negative voltage (-40 to -60V dc) on the analogue input of an Allen Bradley Micrologix 1100 PLC...
Replies
1
Views
2,839
I have been handed two 0-5v pressure transducers with a 0-15psi range and need to connect them to the MicroLogix 1100 analog inputs (0-10v) for a...
Replies
3
Views
3,024
I am using the AB ML1100 PLC's analog inputs for set point control of a pump for both automatic pumping down a vacuum tank and pumping up of a...
Replies
1
Views
2,959
Back
Top Bottom