Old June 12th, 2019, 07:48 PM   #1
Archie
Member
United States

Archie is offline
 
Join Date: May 2002
Location: Orangeburg, SC
Posts: 1,887
Kinextix 300 Not Always Starting on First Try

I have a machine with 14 Kinetix 300 drives communicating via Ethernet/IP. When the program sets the Start Index it does not always start. I had to add a retry timer that drops the signal and re-applies. It repeats this until motion starts. Has anyone experienced this before?

This machine originally had Ultra 100 servo drives and the original programmer also had a piece of reset code that would do the same thing when the drive stopped responding to start signals.
__________________
Expectations lead to disappointment. Appreciation leads to satisfaction.

AdvancedHMI - HMI Software without the license key hassles
  Reply With Quote
Old June 12th, 2019, 07:55 PM   #2
id10t_error
Lifetime Supporting Member
United States

id10t_error is offline
 
id10t_error's Avatar
 
Join Date: Oct 2017
Location: California
Posts: 25
https://rockwellautomation.custhelp....il/a_id/462674

Fault?
__________________
"We make the solutions up out of modules, so they're all standard, ... They're built for security, reliability, ease of expansion and ease of changing. They're the ideas we had many years ago that tend to get lost today." -Ken Olsen co-founded Digital Equipment Corporation (DEC)
  Reply With Quote
Old June 12th, 2019, 07:59 PM   #3
Archie
Member
United States

Archie is offline
 
Join Date: May 2002
Location: Orangeburg, SC
Posts: 1,887
I don't have Tech Connect to view the link.

There are no drive faults.

Turning the Start signal on/off several times always makes it work and no fault reset is ever needed. It's like it just ignores the signal.
__________________
Expectations lead to disappointment. Appreciation leads to satisfaction.

AdvancedHMI - HMI Software without the license key hassles
  Reply With Quote
Old June 12th, 2019, 08:02 PM   #4
Archie
Member
United States

Archie is offline
 
Join Date: May 2002
Location: Orangeburg, SC
Posts: 1,887
Now that I think about it, it got much worst with a faster processor. Maybe the program only turns off the signal for a few scans before re-applying. This would not be enough time to update the IO in the drive which is set to an RPI of 30ms. The new processor scans at 8ms
__________________
Expectations lead to disappointment. Appreciation leads to satisfaction.

AdvancedHMI - HMI Software without the license key hassles
  Reply With Quote
Old June 12th, 2019, 08:08 PM   #5
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 14,699
If your logic doesn't account for asynchronous I/O updates (especially if it removes the Start signal or asserts a Stop signal) then this is the classic way it manifests.

Can you post a screenshot of the index start command logic ?
  Reply With Quote
Old June 12th, 2019, 08:14 PM   #6
Archie
Member
United States

Archie is offline
 
Join Date: May 2002
Location: Orangeburg, SC
Posts: 1,887
The logic maps the IO to account for asynchronous updates. But it does not use a feedback to ensure the start signal was released as seen by the drive before re-applying. I looked at the manual and do not see a corresponding input for the StartMotion output.
Attached Images
File Type: png StartLogic.png (18.1 KB, 41 views)
__________________
Expectations lead to disappointment. Appreciation leads to satisfaction.

AdvancedHMI - HMI Software without the license key hassles

Last edited by Archie; June 12th, 2019 at 08:19 PM.
  Reply With Quote
Old June 12th, 2019, 09:28 PM   #7
Archie
Member
United States

Archie is offline
 
Join Date: May 2002
Location: Orangeburg, SC
Posts: 1,887
I feel like I need to add logic to ensure the StartMotion remains off for at least the RPI. I do not consider adding a timer a very good solution because if the RPI is increased, this will no longer work. I really wish there was an input that would verify the StartMotion signal change made it to the drive before changing it again.

Has anyone else run into this? If so, how did you handle it?
Attached Images
File Type: png StartLogicMod.png (11.6 KB, 37 views)
__________________
Expectations lead to disappointment. Appreciation leads to satisfaction.

AdvancedHMI - HMI Software without the license key hassles
  Reply With Quote
Old June 13th, 2019, 02:02 AM   #8
janner_10
Supporting Member
United Kingdom

janner_10 is offline
 
Join Date: Dec 2014
Location: Tewkesbury
Posts: 738
We have used a few of these drives on smaller projects, looking through past logic, I have put a 500ms delay from the Safety Relay IP to the hardwired enable and the Ethernet enable signals and then another 500ms delay from the Kinetix Enabled IP before any motion move is commanded.

It's been 18 months since our last one, but your problem does ring some bells. A 35ms delay looks a bit keen IMO.
  Reply With Quote
Old June 13th, 2019, 05:27 AM   #9
Archie
Member
United States

Archie is offline
 
Join Date: May 2002
Location: Orangeburg, SC
Posts: 1,887
Quote:
Originally Posted by janner_10 View Post
It's been 18 months since our last one, but your problem does ring some bells. A 35ms delay looks a bit keen IMO.
I chose 35 because the RPI is set to 30ms. That was based on my suspicion being the program can change the state of the outputs faster than the RPI. This machine has a time sensitive cycle so I need minimum delay as possible.

Today I will do some more testing to see if I can find a pattern.
__________________
Expectations lead to disappointment. Appreciation leads to satisfaction.

AdvancedHMI - HMI Software without the license key hassles
  Reply With Quote
Old June 13th, 2019, 06:01 AM   #10
janner_10
Supporting Member
United Kingdom

janner_10 is offline
 
Join Date: Dec 2014
Location: Tewkesbury
Posts: 738
Once it's enabled though, it's enabled so the timer isn't used after that, it just stays on.

Ours is only not enabled when a safety circuit is open, unless you are disabling the drive between moves it won't need to be as fast as 35ms
  Reply With Quote
Old June 13th, 2019, 10:56 AM   #11
RonJohn
Lifetime Supporting Member
United States

RonJohn is offline
 
RonJohn's Avatar
 
Join Date: Jul 2013
Location: NE Ohio
Posts: 469
The last 300 I setup, I had more issues with starting the motion than the other 300's I'd used, probably because this project had more motions occurring more often than the others (RPI = 25ms, by the way). Here's what I learned through tech notes, tech support conversations & lots of testing:

The Kinetix 300 only looks for the .StartMotion 0 ->1 transition

.DriveEn MUST =1, .MotionComplete MUST =1 and .AbortIndex MUST = 0 for the drive to respond to this transition.

Through my own observations I needed to take it a step further and make sure .AbortIndex was off for one scan (One Shot Falling bit) before turning .StartMotion on. I believe this was due to the asynchronous update that Ken mentioned above.

Hope this helps.

Last edited by RonJohn; June 13th, 2019 at 11:03 AM. Reason: added RPI
  Reply With Quote
Old June 13th, 2019, 11:25 AM   #12
Archie
Member
United States

Archie is offline
 
Join Date: May 2002
Location: Orangeburg, SC
Posts: 1,887
I added in the timer to ensure the StartMotion signal was off for at least the RPI. Now everything is working fine.

The RPI was actually 20ms so I used a 25ms timer as a minimum off time for the StartMotion.

So my lesson learned here is that if the program scan is faster than the RPI, be sure the signal does not change faster than the RPI.
__________________
Expectations lead to disappointment. Appreciation leads to satisfaction.

AdvancedHMI - HMI Software without the license key hassles
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
About Starting Diameter Calculation using Position of Web & Spindle a151218 LIVE PLC Questions And Answers 0 March 2nd, 2015 02:45 AM
Kinetix 300 "Active Index" FactoryTalktotheHand LIVE PLC Questions And Answers 4 January 9th, 2015 09:32 PM
Export/Import Textlists WinCC Flex 2008 STL??? LIVE PLC Questions And Answers 6 April 19th, 2010 04:44 PM
S7 300 program in the arj file format DANGELOUS LIVE PLC Questions And Answers 3 February 8th, 2009 12:56 PM
Quick Motion Problems CharlesM LIVE PLC Questions And Answers 3 December 5th, 2006 12:47 AM


All times are GMT -5. The time now is 03:08 PM.


.