I think the issue I take with normally or usually is what defines their normal or usual position? Between that and you would be surprised the people, including instructors, that I have to convince that you don't have to use a "normally open" PLC instruction with an input that has a normally open electrical contact connected to it.
  Reply With Quote
Old June 11th, 2019, 04:21 PM   #17
Operaghost
Member
United States

Operaghost is offline
 
Operaghost's Avatar
 
Join Date: Apr 2002
Location: Dallas, TX USA
Posts: 2,627
Yeah I really dislike "contact" too.

Over the years I taught a lot of people that were familiar with relay logic, and I always tried my best to separate relay logic from ladder logic.

But, everyone sees those symbols and refers to them as contacts. I would avoid that term as well as "normally".

But you just want to slap the people that decided on those symbols and names.

OG
  Reply With Quote
Old June 11th, 2019, 05:21 PM   #18
Bit_Bucket_07
Member
United States

Bit_Bucket_07 is offline
 
Bit_Bucket_07's Avatar
 
Join Date: Feb 2013
Location: Southeast US
Posts: 1,499
I like "AND" for a NO contact and "AND NOT" for a NC contact.
__________________
  Reply With Quote
Old June 11th, 2019, 05:40 PM   #19
jaden
Member
United States

jaden is offline
 
Join Date: Sep 2009
Location: Pleasant Dale, Nebraska
Posts: 167
Normally Open and Normally closed define the state of relay contacts when the coil is not energized or sitting out on a table top. PLC "ladder" logic was meant to represent Relay Ladder symbology. If it is followed through, it is all consistent.
  Reply With Quote
Old June 12th, 2019, 01:01 AM   #20
ivo.maenen
Member
Belgium

ivo.maenen is offline
 
ivo.maenen's Avatar
 
Join Date: Nov 2003
Posts: 649
Quote:
Originally Posted by jaden View Post
Normally Open and Normally closed define the state of relay contacts when the coil is not energized or sitting out on a table top. PLC "ladder" logic was meant to represent Relay Ladder symbology. If it is followed through, it is all consistent.

So if I wire a NC-stop-pushbutton to an input and a NO-start pushbutton


being consistent means you would program something like (I do not use the seal-contact!):


STOP START motor

--|/|----| |----( )


Thats not logical to me.....




I prefere:


-| |- : OK if status '1'



-|/|- : OK if status '0'
__________________
Assumptio mater errorum est.
  Reply With Quote
Old June 12th, 2019, 04:48 AM   #21
Gene Bond
Member
United States

Gene Bond is offline
 
Join Date: May 2004
Location: Indianapolis, IN
Posts: 349
The voices in my head say, "If On" or, "If NOT On", when I'm reading a ladder rung...
  Reply With Quote
Old June 12th, 2019, 05:13 AM   #22
Rson
Member
United States

Rson is offline
 
Join Date: Jun 2017
Location: Michigan
Posts: 175
Quote:
Originally Posted by ivo.maenen View Post
So if I wire a NC-stop-pushbutton to an input and a NO-start pushbutton


being consistent means you would program something like (I do not use the seal-contact!):


STOP START motor

--|/|----| |----( )


Thats not logical to me.....




I prefere:


-| |- : OK if status '1'



-|/|- : OK if status '0'
If you use relay logic terms or are used to it, it is still consistent.

For example, if I wanted to take 1 contact and make it many in relay logic, I would wire (for instance) a NC contact to a relay, and then all of my logic would be reversed on the relay’s contacts (since the relay would be ‘on’ in the normal condition)

I think preferred terminology all comes down to who has used relay logic (which PLCs were made to replace, and thus use NO, NC, and COIL contacts in ladder) or if you are approaching it as PLC-centric (on/off from the PLC’s point of view)
  Reply With Quote
Old June 12th, 2019, 05:15 AM   #23
Mad_Poet
Member
United States

Mad_Poet is offline
 
Join Date: Feb 2017
Location: Virginia
Posts: 374
Jaden > Normally Open and Normally closed define the state of relay contacts when the coil is not energized or sitting out on a table top. PLC "ladder" logic was meant to represent Relay Ladder symbology. If it is followed through, it is all consistent.

>>>

I am in agreement with Jaden on this.
What little PLC programming I have done is in ladder. And NC or NO contacts make
perfect sense. If the 'contact' is an input, the NC type means if there are no
volts on that input give me 'continuity' through the contact on the rung and if
it is the NO type then one must have volts on the input to get continuity through
the rung.

When monitoring a running PLC program in ladder logic everything 'works'
properly if looked at as energized coils close NO contacts . . At least in Allen
Bradley the closed contacts (allowing continuity) are obvious.
Poet.

Last edited by Mad_Poet; June 12th, 2019 at 05:17 AM. Reason: Made a NO NC. Corrected.
  Reply With Quote
Old June 12th, 2019, 05:39 AM   #24
LadderLogic
Member
United States

LadderLogic is offline
 
LadderLogic's Avatar
 
Join Date: Jun 2003
Location: Chicagolandia
Posts: 1,320
The whole reason for the existence of PLCs, as opposed to other computer systems, was the concept of representing Boolean logic via elements of electrical circuits: contacts, relays, timers and counters. This is what made the PLCs so ubiquitous: making programming understood by electricians. Structured text and other more advanced methods appeared later, with the goal of overcoming the obvious shortcomings of Ladder approach.

Therefore, when explaining PLCs, one cannot skip the ladder representation even if it is not meant to be used in the future. And in the electrical world terms "normally open" and "normally closed", NO and NC, have existed for more than hundred years and have become de-facto standard understood by everyone. I think any deviation from them even when describing a bit in memory rather than a physical contact will just muddy the waters. Do not overthink it.
__________________
Don't trust, don't fear, don't beg...
  Reply With Quote
Old June 12th, 2019, 06:13 AM   #25
saultgeorge
Lifetime Supporting Member
United States

saultgeorge is offline
 
Join Date: Jul 2015
Location: Detroit
Posts: 217
+1 for LadderLogic.
I agree with those statements 100%. I was an industrial electrician for years before doing all programming, and of course I started out in hard-wired relay logic. And A-B ladder is easy for me to program in, easy to understand and also easy to explain to others. I am working on ST and a lot of other platforms like CodeSys, but A-B will always be my comfort level.
__________________
4 out of 5 Great Lakes prefer Michigan.

Last edited by saultgeorge; June 12th, 2019 at 06:14 AM. Reason: typo
  Reply With Quote
Old June 12th, 2019, 06:24 AM   #26
Ron Beaufort
Lifetime Supporting Member
United States

Ron Beaufort is offline
 
Ron Beaufort's Avatar
 
Join Date: Jul 2002
Location: Charleston, SC
Posts: 5,540
rankhornjp nailed it back in Post #7

Quote:
That symbol means "Go look for a 1"
I've been teaching this "better mousetrap" explanation for about twenty years now - and the world (from even as far away as Australia) has truly beaten a path to my door ...

this approach allows you to teach the concepts to ANYONE (who's willing to learn) whether they have any previous electrical or PLC experience or not ...

the following YouTube is the first in a series of eleven ... these should all be watched in number order - since they all make up one 90-minute lesson ...

https://www.youtube.com/watch?v=T3tnXu-Eywc

I've lost count of how many schools have asked me for permission to use this series of videos as part of their curriculum - and I know for a fact that many others around the world are using them without bothering to ask for permission (and that's OK with me) ...

now that I'm finally retired, I welcome anyone to use them free of charge - as long as they are shown in their entirety - including the copyright notices and credits ...
__________________

2-B ?
Best regards, ----+----] [----+------------( )----
Ron | |
PLC Training Boot Camp - Retired | 2-B |
+----]/[----+

I once was lost, but now am found, was blind, but now I see.


Last edited by Ron Beaufort; June 12th, 2019 at 06:52 AM.
  Reply With Quote
Old June 12th, 2019, 06:41 AM   #27
parky
Member
United Kingdom

parky is offline
 
Join Date: Oct 2004
Location: Midlands
Posts: 1,232
I'm Old school (well at my age it's got to be). PLC's were considered a replacement of all those hard wired relays (and logic blocks) so I still use normally open & normally closed that is in their non energised state. IEC is just a continuation of Boolean logic symbols so like AND x AND Not Y OR etc.
examine if open seems a bit alien to me examine if open suggests check if it is open so as I see it a normally open contact (not energised) then it is not true so will not perform the function (sounds a bit backward to me).
Relays with multi contacts are normally described as 2 NO 2 NC so normally open = ----! !---- so in my book this is normally open (can of worms here I'm sure and I suspect the AB guru's out there will have their penny's worth).
  Reply With Quote
Old June 12th, 2019, 08:27 AM   #28
geniusintraining
Lifetime Supporting Member + Moderator
United States

geniusintraining is offline
 
geniusintraining's Avatar
 
Join Date: Jun 2005
Location: SC
Posts: 6,439
Tim, I have been doing electrical now for a few days... I have never heard anyone use "Usually" and I am from the South and they will make up their own words down here.

Side note: Siemens STL is (was) the best AND, NOT, AND NOT.... never confusing
__________________
www.PLCCable.com PLC Communication Cables, PLC Trainers, Fluke Meters, MicroLogix, ControlLogix, Siemens, Allen Bradley and more... all your automation needs... ((NEW)) After Market 1784-U2DHP Allen Bradley USB to DH+ and Gateways
  Reply With Quote
Old June 12th, 2019, 09:19 AM   #29
TWControls
Lifetime Supporting Member
United States

TWControls is offline
 
TWControls's Avatar
 
Join Date: Oct 2005
Location: Roanoke, VA
Posts: 2,142
Here's the video, let me know what you think.
PLC Instructions are not the same as Electrical Symbols | Normally Open and Normally Closed?
https://youtu.be/ZuXUo8PfcDw
  Reply With Quote
Old June 12th, 2019, 01:05 PM   #30
g.mccormick
Lifetime Supporting Member
United States

g.mccormick is offline
 
Join Date: Jul 2012
Location: IN
Posts: 637
Quote:
Originally Posted by geniusintraining View Post
Tim, I have been doing electrical now for a few days... I have never heard anyone use "Usually" and I am from the South and they will make up their own words down here.

Side note: Siemens STL is (was) the best AND, NOT, AND NOT.... never confusing
So do you use the terms "cut it on" and "cut it off" instead of turn on and turn off?
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Need help for drawing PLC ladder diagram mayank_04081989 LIVE PLC Questions And Answers 8 November 20th, 2012 11:18 PM
plc ladder diagram mayank_04081989 LIVE PLC Questions And Answers 4 November 15th, 2012 01:12 PM
Flow diagram -> ladder diagram HELP alehander LIVE PLC Questions And Answers 44 April 18th, 2008 03:53 AM
need a ladder diagram....Help please.... dawghogston LIVE PLC Questions And Answers 2 April 12th, 2003 06:38 AM
Communication between Ladder Diagram and PLC sandhu LIVE PLC Questions And Answers 5 December 15th, 2002 11:56 PM


All times are GMT -5. The time now is 06:47 PM.


.