MicroLogix 1200 Connecting to PV 800

Ryan_Flowers

Lifetime Supporting Member
Join Date
Feb 2019
Location
Las Vegas
Posts
57
Hello,

I have a MicroLogix 1200 controller that I'm trying to get to communicate with a PV 800 (CAT 2711R-T4T). This mostly likely means that I must use the serial port to connect via the DF1 driver and configure the PV to do so. The PV has to be 25 feet from the conntroller and I obviously cannot buy the 1761-CBL-PM02 to the length I need. So this led me to buy some cable and put the necessary connectors on both ends. I also believe I pinned the din and serial connectors correctly.

The main problem is that I cannot see my PV 800 in RsLinx when I connect directly to it, much less will my controller be able to see it. In the terminal itself, the configuration is for the serial port and the ethernet is disabled.

What could I be doing wrong?

Thanks
 
Have you loaded a program into the PV800? The serial port may be active but until you load a program the serial port isn't configured for any particular protocol.
 
Do yourself a favor and replace the 1200 for a 1400 and go Ethernet, if you have additional I/O it will fit on the 1400. Depending on the model should be under $400
to get a clean used one.
 
The PanelView 800 connects directly to a MicroLogix 1200 with the equivalent of a 1761-CBL-PM02 cable, so that means that the DB9 RS-232 port on the PanelView 800 terminal must be the same kind as on your PC, a "DTE" type port. You would use a "null modem" type cable to connect it to a PC.

Most folks use Ethernet, or the USB cable (which emulates an Ethernet connection using TCP/IP), to connect to the PanelView 800 for download.

I admit I'm not sure if you even *can* download over the RS-232 port to the PanelView 800.
 

Similar Topics

Hi there I am new with this thing and i don't know how to connect Allen Bradley Micrologix 1200 PLC to Raspberry Pi using USB to RS485 in NodeRED...
Replies
3
Views
2,260
First of all Hi, nice to met you all. I have a problems trying to control my PLC's (1762-L40BWA ser. C and 1763-L16DWD ser. B) with the Panelview...
Replies
10
Views
5,028
I would like to know if it is possible to connect a Panelview 1000 (cat 2711-T10C8) that has DH+ to a micrologix 1200 with or without a AIC +...
Replies
1
Views
2,216
Hi. Its been a long time since the last time I used the rslogix500 to connect to a plc and seems that I forgot how to do it. I opened the rslinx...
Replies
2
Views
2,152
I must admit it has been some time since my college days and I really haven't retained much since then. I am looking for some assistance with...
Replies
2
Views
2,546
Back
Top Bottom