My opinion is this.
"Aux input" should mean that the contactor is pulled in. If you want to add another input to the PLC to say "at speed" then add it as an extra input, not as a replacement to the aux input.
Now, the question:
How do I support my opinion?
Is my opinion valid?
Many customers don't realize the implications of changing the parameter on the Variable Frequency drive from "running" to "running at speed" after the program has been written. They think that just increasing a timer in the "Motor Failed to Run" section of my plc program is a cure all. Some times this is not the case.
While trying to follow the "Customer is always right" philsophy, should I write my programs with the intention that this contact could perform either way?
It was a bigger deal when I was working in the packaging industry. Many conveyors that were moving parts into position would never get up to speed. The plc need to know that the conveyor was moving. I was able to support my argument very well then, and could pretty much demand that the parameter be changed back to drive running.
Now, I am in the gas and oil industry. This is a new industry for me, and I may be making a big deal out of nothing. The thing that bothers me the most, though, is when I write the program thinking "drive running", only to find out later that the contact is really "running at speed".
So, I need to know if I should write my programs for either scenario. (is this even possible?).Or, should I argue my case and demand one or the other. Am I making too big a deal out of nothing? Has anyone else ran into the same problems?
One example:
I can think of one example from an earlier post where Allen Case mentioned to place the N.C. state of the aux contact from the FWD starter in series with the Motor Run Coil of the REV starter and vice versa, instead of just using N.C. of the opposing PLC Run Coils. I think that this is a good idea. I think that this would prevent the PLC from trying to energize the REV coil if the FWD coil was stuck in, or if someone was holding it closed with their fuse pullers. Even though I believe that these reversing contactors are usually mechanically interlocked. - Now, how would this logic work if the "at speed contact were being used".
"Aux input" should mean that the contactor is pulled in. If you want to add another input to the PLC to say "at speed" then add it as an extra input, not as a replacement to the aux input.
Now, the question:
How do I support my opinion?
Is my opinion valid?
Many customers don't realize the implications of changing the parameter on the Variable Frequency drive from "running" to "running at speed" after the program has been written. They think that just increasing a timer in the "Motor Failed to Run" section of my plc program is a cure all. Some times this is not the case.
While trying to follow the "Customer is always right" philsophy, should I write my programs with the intention that this contact could perform either way?
It was a bigger deal when I was working in the packaging industry. Many conveyors that were moving parts into position would never get up to speed. The plc need to know that the conveyor was moving. I was able to support my argument very well then, and could pretty much demand that the parameter be changed back to drive running.
Now, I am in the gas and oil industry. This is a new industry for me, and I may be making a big deal out of nothing. The thing that bothers me the most, though, is when I write the program thinking "drive running", only to find out later that the contact is really "running at speed".
So, I need to know if I should write my programs for either scenario. (is this even possible?).Or, should I argue my case and demand one or the other. Am I making too big a deal out of nothing? Has anyone else ran into the same problems?
One example:
I can think of one example from an earlier post where Allen Case mentioned to place the N.C. state of the aux contact from the FWD starter in series with the Motor Run Coil of the REV starter and vice versa, instead of just using N.C. of the opposing PLC Run Coils. I think that this is a good idea. I think that this would prevent the PLC from trying to energize the REV coil if the FWD coil was stuck in, or if someone was holding it closed with their fuse pullers. Even though I believe that these reversing contactors are usually mechanically interlocked. - Now, how would this logic work if the "at speed contact were being used".