Is there a way to make a 'virtual' S7 CPU - PLCSIM for instance - talk to real I/O via a CP5512 profibus card? Or is there another package other than PLCSIM that can do this?

I need to QC some panels being built by a local panel shop. The testing protocol calls for me to verify every input and output live. I normally do this by taking my laptop and a CPU rack over to the panel shop, building a test configuration in the CPU rack, connect it via profibus to each rack I'm testing, activate every input and watch it turn on in the online hardware view, then force every output and verify that the output actually turns on and gives me a voltage.

I don't need to run any logic; I JUST need to verify that the hardware is 100% okay and wired correctly.

Is there a way to accomplish this same task using just my laptop, a CP5512 profibus card, and whatever software, WITHOUT also having an actual CPU in the loop ?
 
If you have Softnet S7 Profibus, then you can setup a "PC Station" with OPC Server. This will allow you to let the "PC Station" be a Profibus master. Any OPC Client can then address the configured i/o. The "OPC Scout" test client for example can do it.
 

Similar Topics

Hi All, Is a 315 2 PN CPU supported in PLCSim Tia Portal V13 ? Seems that it only works with a 1500 or is that wrong ? Thanks, Kind regards, G
Replies
7
Views
3,803
Hi Why does this code not working in a CPU 416-2 ? FUNCTION_BLOCK FB840 TITLE = 'Read and write to Kval-DB' // // Block Comment... // VERSION...
Replies
22
Views
281,598
Is it possible via Ethernet (CP443)? I know I can run communication between two PLCSIMs V5.4 , but the task is to get it talking to the real CPU.
Replies
0
Views
86,635
How to simulate 2 cpu using Step7 plcsim i tried with no success i followed this guide here...
Replies
4
Views
90,818
Is it possible to test S7-communication (BSEND BRECEIVE) between two S7 315PN cpu's or is it only possible with 400 PLC's. In my tests it worked...
Replies
2
Views
4,733
Back
Top Bottom