All Blacks said:
PF525 Pld...maybe PLe...?

FYI you can get PLe from Cat 3...

...Also if you look at the PF525 safety data...it can get PLe as well?...

Hi,

There is no maybe...

You may have not read or missed the meaning in some of my earlier statements but I had already stated that you can achieve PLe using a PowerFlex 525 with STO, but not on its own. To explain it again more simply and without the functional safety data calculations you have provided...

Geospark said:
...the PowerFlex 525, using Safe Torque-Off, can achieve SIL 2 Category 3 /PLd alone...

This means when used on its own the PowerFlex 525 can achieve a maximum Performance Level of PLd.

However...

Geospark said:
...To achieve SIL 3 Category 3 / PLe, STO would have to be used in conjunction with other Safety measures to achieve this higher Performance Level.

You need to know which Performance Level (PL) you require here before deciding whether or not it is permissible to use STO only on these drives.

That is, you may or may not need Safety contactors here. PLd, for instance, may permit the use of no contactors here...

What this essentially means is that if PLd is required, then the PowerFlex 525 with STO can achieve this Performance Level without using Safety contactors. If Performance Level PLe is required then the PowerFlex 525 with STO can be used in conjunction with Safety Actuators i.e. Safety contactors.

So yes, Performance Level PLe is achievable using the PowerFlex 525 as part of an overall Safety Function.

But now, back to the functional safety data calculations...

522301 - How do I achieve PLe with a PowerFlex 525 drive
Access Level: Everyone

From here we can see that it is possible to achieve SIL 3 Cat 3 PLe based on a Probability of dangerous Failure per Hour (PFHd) scoring of 5.8 e-8. This equates to a Probability of dangerous Failure per hour of < 0.00000058%

"e"asy...

Regards,
All Green
 

Similar Topics

Good Morning , I'm building a control panel with PowerFlex 525 drives. I have black wire for the 480 vac , red for 110 vac , blue for 24 vdc...
Replies
7
Views
2,895
Hello, If I am controlling a PF525 through ethernet (Start + Speed commands) and If by coincidence the start command is ON and a Safe Torque OFF...
Replies
0
Views
3,487
Hi to all. We need to change a bad powerFlex 525 to a new one. How do you save the configuration to install in the new one? Thank you all for...
Replies
5
Views
220
Im trying to teach a couple of labs on VFDs at a community college. We have some motor control trainers with P525s and 3 phase motors from...
Replies
2
Views
227
New to vfds. I put in parameters. IP, but I get ethernet flashing and link solid. What did I do wrong?
Replies
9
Views
458
Back
Top Bottom