Modbus Vs direct io on vfd

Hi all is there any hard and fast rule on using modbus vs direct io for controlling vfd's from a plc? I'm looking at using modbus to control 6 vfd from a plc to reduce the amount of io needed on the plc. Are there any big issues I need to worry about doing it this way?
Regards
Beau
  Reply With Quote
Old March 17th, 2018, 06:37 AM   #2
Saffa
Member
New Zealand

Saffa is offline
 
Join Date: Feb 2012
Location: Bay of Plenty
Posts: 941
The main thing to consider is what happens if you lose communications between your PLC and the drive.

Most drives have the ability to detect when commands are no longer being written and can go to a safe state. Make sure this is enabled, and test that it works.
  Reply With Quote
Old March 17th, 2018, 11:22 AM   #3
Tom Jenkins
Lifetime Supporting Member
United States

Tom Jenkins is offline
 
Tom Jenkins's Avatar
 
Join Date: Apr 2002
Location: Milwaukee, WI
Posts: 5,920
There are few hard and fast rules about anything.

However, when I've used a comm link to control the drive I always had a hard-wired signal from my E-Stop and critical run permissive contacts. This would include things like lube oil pressure switches or a NC contact from the PLC. That protects the equipment even if the comm link goes down or is slow. You still have equipment protection.
  Reply With Quote
Old March 17th, 2018, 12:22 PM   #4
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 9,982
Responsiveness is another consideration. How fast do your drives need to react to a change in the command? If the application can tolerate a couple of seconds delay from the VFDs then it can work. I do a lot of water pumping applications where it makes good sense to use Modbus RTU because it doesn't matter if the drives are a few seconds late changing speeds or starting or stopping.

Also, if at any time one or more of the drives is powered down, your PLC messages will error which will add a considerable amount of time to the polling cycle for those that are still up and ready.

All the VFDs I have worked with have a communication timeout action and delay. So you can program what you want the drive to do and how much time between polls is considered a communication loss.
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.
  Reply With Quote
Old March 17th, 2018, 12:36 PM   #5
lfe
Member
France

lfe is offline
 
Join Date: Jun 2007
Location: Barcelona
Posts: 306
I always used a timeout timer, the timer begins to count when I send the request and it's reset when I get the correct reply, if the time expires then I switch off via contactors the concerned equipment.
__________________
Suppanel HMI
  Reply With Quote
Old March 17th, 2018, 12:51 PM   #6
janner_10
Supporting Member
United Kingdom

janner_10 is offline
 
Join Date: Dec 2014
Location: Tewkesbury
Posts: 667
If Modbus is native to both PLC and Drives, then there isn't really a reason why not.

The PLC type and drive type would be of help though.
  Reply With Quote
Old March 17th, 2018, 04:06 PM   #7
rupej
Member
United States

rupej is offline
 
Join Date: Sep 2014
Location: NC
Posts: 429
Only reason against modbus would be possible added complexity for the maintenance people that have to live with it, and harder to swap to a different model/brand of drive later on.

In other words, it makes it less "generic"
  Reply With Quote
Old March 17th, 2018, 07:24 PM   #8
Beau79AU
Member
Australia

Beau79AU is offline
 
Join Date: Feb 2018
Location: NSW
Posts: 11
Thanks for the replies. Will most likely be Schneider m221 plc and Schneider atv630 drives as we already have some of these drives. It is for running grout mixing barrels and pumps so a couple of seconds delay wont be too much drama.
Regards
Beau
  Reply With Quote
Old March 18th, 2018, 12:44 AM   #9
Saffa
Member
New Zealand

Saffa is offline
 
Join Date: Feb 2012
Location: Bay of Plenty
Posts: 941
The M221 supports IOScanning of drives over Ethernet, if you have the model with Ethernet port.

Do a Google search for "M221 IOScanning", there's a video showing setup for an ATV320 but similar process for ATV630.

Much easier than rolling your own, given how clunky SoMachine is compared to Unity.
  Reply With Quote
Old March 18th, 2018, 04:24 AM   #10
(8{)} ( .)
Lifetime Supporting Member
Israel

(8{)} ( .) is offline
 
(8{)} ( .)'s Avatar
 
Join Date: Apr 2004
Location: Israel
Posts: 590
We generally start and stop the drive with digital I/O. All the rest is handled over the network whether it's ModbusRTU, ModbusTCP, or ModbusUDT. If your PLC supports ModbusUDT then use that. No reason to use ModbusTCP to communicate with a drive unless it's the only ethernet protocol it supports.

Good Luck,

Yosi
  Reply With Quote
Old March 18th, 2018, 02:23 PM   #11
danw
Member
United States

danw is offline
 
danw's Avatar
 
Join Date: Oct 2004
Location: midwest, USA
Posts: 2,833
Quote:
Originally Posted by (8{)} ( .) View Post
We generally start and stop the drive with digital I/O. All the rest is handled over the network whether it's ModbusRTU, ModbusTCP, or ModbusUDT. If your PLC supports ModbusUDT then use that. No reason to use ModbusTCP to communicate with a drive unless it's the only ethernet protocol it supports. Yosi
I'm going to start a new topic because I see differences in RTU vs TCP for the hardware layer implementation and I'm curious as to who implements Modbus UDT and whether it is as 'reliable' as Modbus/TCP.
  Reply With Quote
Old March 18th, 2018, 02:51 PM   #12
lfe
Member
France

lfe is offline
 
Join Date: Jun 2007
Location: Barcelona
Posts: 306
UDT or UDP ?
if it is really UDP then by definition it is less reliable than TCP, since using UDP the sender has no confirmation that the packet has really been received at the other end.
The advantage is that it can be faster than TCP.
__________________
Suppanel HMI
  Reply With Quote
Old March 18th, 2018, 04:48 PM   #13
Pete.S.
Member
United States

Pete.S. is offline
 
Join Date: Mar 2016
Location: Fl
Posts: 464
Quote:
Originally Posted by Beau79AU View Post
Hi all is there any hard and fast rule on using modbus vs direct io for controlling vfd's from a plc? I'm looking at using modbus to control 6 vfd from a plc to reduce the amount of io needed on the plc. Are there any big issues I need to worry about doing it this way?
Regards
Beau
Safety - as modbus is not a safety protocol so you can't transfer STO signals for instance.

Portability - you will be dependent on a specific model or brand VFD in your application.

Troubleshooting - if something is not working bus protocols are extremely hard to troubleshoot for electricians.
  Reply With Quote
Old March 19th, 2018, 01:18 AM   #14
(8{)} ( .)
Lifetime Supporting Member
Israel

(8{)} ( .) is offline
 
(8{)} ( .)'s Avatar
 
Join Date: Apr 2004
Location: Israel
Posts: 590
Quote:
Originally Posted by lfe View Post
UDT or UDP ?
if it is really UDP then by definition it is less reliable than TCP, since using UDP the sender has no confirmation that the packet has really been received at the other end.
The advantage is that it can be faster than TCP.
My typo...

Thanks for the correction.
  Reply With Quote
Old March 19th, 2018, 04:28 AM   #15
BryanG
Member
United Kingdom

BryanG is offline
 
Join Date: Feb 2005
Location: Manchester
Posts: 1,291
One big advantage of modbus is that you will probably be able to grab a load of data from the VSD, not just control it. I don't know the Schneider drives so I don't know what data is available, in ABB you can get all the drive running data. Would it be helpful to know what power the drive is pulling, would it give you an idea of how the mixing process is going. We are no longer 'just' PLC programmers we also collect 'big data' to try to spot trends in machine data and improve efficiency.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Direct Logic 205 PLC - Modbus TCP Help edward.ortiz LIVE PLC Questions And Answers 3 June 29th, 2015 09:55 AM
Help for Delta DVP-SC series PLC and LS iG5A VFD Modbus communication kam LIVE PLC Questions And Answers 0 March 25th, 2012 03:31 AM
SMC EX250-SEN1 modbus TCP and IO scanning with Quantum PLC Code17 LIVE PLC Questions And Answers 0 June 10th, 2009 10:36 AM
Seimens VFD issue ascot01 LIVE PLC Questions And Answers 5 February 14th, 2009 11:19 PM
modbus communication b/w wago RS232 module and Automation direct HMI Siby LIVE PLC Questions And Answers 2 October 13th, 2008 09:00 AM


All times are GMT -5. The time now is 04:07 PM.


.