What you could do is convert the PLC2 program directly to RSLogix 500 (manual conversion), then swap the PLC2s to SLC 500s. This would be a long-term project to be done in steps, so you do not disrupt the factory.Got you. Damn I wish RS Logix 500 could be use with PLC-5. Then I could get RS Logix 500 and covers all basis here and convert to PLC-5 for this machine.
1. Convert the PLC2 programs to RSLogix 500 (or hire contractor to do it for you- maybe $500 per program depending on size).
2. Install a SLC 500 next to the first old PLC2.
3. During downtime, swap the I/O wiring over to the SLC 500.
4. Test the new program, debug, and start it up.