Comms fail action (M340 <-> STB NIP2212)

iJAF

Member
Join Date
Sep 2010
Location
PT
Posts
14
Hi !

Hi have a M340 connected to several NIP2212 STBs !

If i disconnect the network cable from any STB, they enter in fail mode and make the predefined action (outputs to 1 or 0) immediately !!!

My question:

is there any way to delay 10 seconds the outputs from entering in fail mode ?! i.e. they only make the predefined action if the cable is disconnected more than 10 secs !

Thanks in advance !!
 
On the webpage for the NIP2212, select

Configuration -> Master Controller -> Holdup time

I didn't try it, but I expect this to delay fallback action.
 
On the webpage for the NIP2212, select

Configuration -> Master Controller -> Holdup time

I didn't try it, but I expect this to delay fallback action.


Thank you !!! it worked :)

i was only checking in advantys and not in web configuration pages !!!
 

Similar Topics

Hi, I am wanting to generate an alarm in the HMI if comms to the PLC is interrupted for any reason. I know I can use system diagnostics, but...
Replies
0
Views
1,242
I am working on setting up a Prosoft Datalogger model PLX51-DLplus-232. This unit will be collecting data from a SLC 5/05 on the DB9 port set to...
Replies
3
Views
80
Hello, can someone share/explain How to check comms between PC and PLC via TeamViewer? TIA
Replies
14
Views
379
Has anyone setup communications with Red Lion 3.0 MODBUS to Baker Hughes Centrilift GCS VFD? Thanks
Replies
0
Views
81
Hi , Looking for some help. We have a 343-1 PN Lean Card & 315-2DP connected to an external system collecting data. After a recent shutdown...
Replies
0
Views
59
Back
Top Bottom