Hi everyone,

I ran into a problem today when wiring my PLC (Mitsubishi Melsec FX-32MR) which has 17 inputs and 17 relay type outputs.

I have 3 Solenoid Valves and 3 Bilge Pumps (all 12v), and I have 9 indication lamps (24V)
My problem is if i allocate COM 1 and COM 2 to 12V Outputs and COM 3 and COM 4 to 24V outputs. I only have 8 24V outputs and I need 9.

I could get a 12V lamp but they're quite expensive or else they wont arrive by the time ive to demo this project, could I do anything else with this?

Thank you

Also,sorry if this question is stupid I've just hit a wall with this problem

29634948_2092373360803452_4848710_o.jpg
 
note that you don't have 17In 17 out, you have 16 in 16 out..
0..17 in octal = 0..15 in decimal

Wire them all 24V and use 24V relays for your 12V stuff.

You don't mention the spec of your valves and pumps, but use that to work out what size relay you need.

6 of these, for example.
https://uk.rs-online.com/web/p/non-latching-relays/1357375/

If you're tight up for cash, you can buy just two of these, and wire the other 4 outputs through your PLC via COM1 or whatever.

For future, 24V is more standard in industrial applications if you can avoid 12V products.

Another option is to have one of your LEDs never come on :p
 
Thank you

Thanks guys. I wish I knew 24V components would of made my life easier but I guess I've learned a valuable lesson from this :)

I will be able to get 24V relays from the college thankfully.
 
An LED indicator rated at 24Vdc will still light at 12V, just not as bright. This is how I fixed the backlight in the clock in my car.
 

Similar Topics

Good Morning , I installed an AC Tech ESV 1 HP Drive on a small bucket conveyor. Before it had a DC Motor on it . It now has a Baldor 1 HP...
Replies
1
Views
207
I am running Logix Designer v32, and noticed if I type new instruction value(s) (XIC, XIO, MOV, etc etc) into a rung without any operands/tags...
Replies
4
Views
757
Hi everyone,im using delta dvp12se11r,for first time setting ethernet ip is dcisoft software is enough?.im using ispsoft for programming and...
Replies
0
Views
396
Hello all. I have a 5069-L306ERMS2 that is interfaced with an ABB IRC palletizing robot. I am having trouble metering cases to the pick point...
Replies
4
Views
1,863
A bit of background here: We use an incremental encoder with a counting module in our PLC configuration. Using dual phase / quadrature counting...
Replies
26
Views
8,911
Back
Top Bottom