HMI - Volume of irregular shaped Tank

Hi experts

I got a last minute surprise when the customer told me that the tank is not uniform

I already have program which show this on scale of 0 to 100% but it has to be changed to actual Volume which is around 85 units of Volume (gallon)

The Customer has been using a float ball type Potentiometer based Level sensor it has an output of 0 to 5 Volts DC - and my module is 0 to 10 V DC analog input

this is being Used to measure the volume of fluid inside the tank, the tank is having a shape as shown in the picture
https://imgur.com/gallery/YcjIN9d
How do I tackle this issue?

Last edited by qwemx; October 31st, 2019 at 01:04 PM.
  Reply With Quote
Old October 31st, 2019, 01:08 PM   #2
widelto
Member
Colombia

widelto is offline
 
widelto's Avatar
 
Join Date: Jul 2005
Location: Barranquilla, Colombia
Posts: 2,829
Is lower part a cylinder ??
Is upper part a cylinder ??
__________________
My two cents.
  Reply With Quote
Old October 31st, 2019, 01:10 PM   #3
Elcan
Member
United States

Elcan is offline
 
Join Date: Apr 2008
Location: NC
Posts: 839
You have to create a formula, calculating the volume for each of the tank sections, using an IF or a Greater Than condition.
  Reply With Quote
Old October 31st, 2019, 01:29 PM   #4
qwemx
Member
India

qwemx is offline
 
qwemx's Avatar
 
Join Date: Jul 2017
Location: UAE
Posts: 119
Quote:
Originally Posted by Elcan View Post
You have to create a formula, calculating the volume for each of the tank sections, using an IF or a Greater Than condition.
Something like this

IF output_from_the_sensor is less than height of smaller part THEN Volume :=((real value from sensor )/Real_Value_till_the_ball_is_inside_the_Lower_Part) *Total_height_of_lower_part*Volume_Per_Unit_Height ));
Else
Volume := (ReaL Value from sensor - Real_Value_till_the_ball_is_inside_the_Lower_Part) * Volume_of_upper_part_perunitheight)+ Total_volume_of_the_lower_Part.

Main variables to investigate

Till what height is the lower part, what reading it reads on the level sensor and what is the total volume of this part

What is the height of the Upper part
what value the Sensor reads on reaching 100%

Last edited by qwemx; October 31st, 2019 at 01:35 PM.
  Reply With Quote
Old October 31st, 2019, 01:30 PM   #5
qwemx
Member
India

qwemx is offline
 
qwemx's Avatar
 
Join Date: Jul 2017
Location: UAE
Posts: 119
Quote:
Originally Posted by widelto View Post
Is lower part a cylinder ??
Is upper part a cylinder ??
I will check the drawings. I did not receive anything yet.
  Reply With Quote
Old November 1st, 2019, 06:56 AM   #6
alfhuckett
Member
United Kingdom

alfhuckett is offline
 
Join Date: Jan 2018
Location: home
Posts: 6
The float sensor gives 0-5V output, This is based purely on the height of liquid in tank.


Treat the tank as two sections, and work on the dimensions of each section.


e,g Lower Section A, 40% of Height; Upper Section B, 60% of height


If Sensor Output <2 Volt, Volume = V/2 x Volume A
If Sensor Output >2 Volt, Volume = ((V-2)/3) x Volume B)+ Volume A


Adjust the numbers to suit the relative heights of the sections.
  Reply With Quote
Old November 1st, 2019, 07:01 AM   #7
cjd1965
Member
United Kingdom

cjd1965 is offline
 
Join Date: Apr 2007
Location: UK
Posts: 1,568
you may need to pour in known amounts like 50 litre steps and record the potentiometer reading and then create a table in the PLC to lookup the values vs litres / gallons
  Reply With Quote
Old November 1st, 2019, 07:13 AM   #8
AustralIan
Member
Germany

AustralIan is offline
 
Join Date: Jan 2013
Location: Germany
Posts: 1,118
Oh and when you say Gallon, you have to say US Gallon or Imperial Gallon, otherwise International Weights and Measures finds you and they do things to you.

cjd1965 has it right. At the very least you should test it like this.
0-5V potentiometer on a float sounds like it won't be linear either.
  Reply With Quote
Old November 1st, 2019, 07:27 AM   #9
roxusa
Lifetime Supporting Member
United States

roxusa is offline
 
Join Date: Nov 2008
Location: NJ
Posts: 767
I use these mounted on top of tank facing down.
https://www.automationdirect.com/adc...suring/opt2011
They are much more accurate 0-10 v although as others have stated you will need
2 formulas to get the volume one for lower section and one for top. I would write 2 separate SCP's with a GTR to switch between them
__________________
B.Pedersen
if you are going to assume, assume you're wrong.
  Reply With Quote
Old November 1st, 2019, 10:14 AM   #10
cardosocea
Member
United Kingdom

cardosocea is offline
 
Join Date: Nov 2016
Location: Fields of corn
Posts: 1,540
Does the oddly shaped tank's mechanical drawings or documentation include a "sounding table"?

It's definitely not the same, but for quite a few of ballast tanks in ships, the manufacturer will supply you with this sort of table that lists volume per cm of liquid inside it. It's then fairly easy to detect transition points and come up with a formula to calculate the volume.
  Reply With Quote
Old November 1st, 2019, 10:57 AM   #11
qwemx
Member
India

qwemx is offline
 
qwemx's Avatar
 
Join Date: Jul 2017
Location: UAE
Posts: 119
Yes I have a sounding table
  Reply With Quote
Old November 1st, 2019, 11:18 AM   #12
qwemx
Member
India

qwemx is offline
 
qwemx's Avatar
 
Join Date: Jul 2017
Location: UAE
Posts: 119
Sorry Volume has to shown in Barrels .
more details in documents
sounding table and dead volume also because if the ball type sensor
https://www.dropbox.com/sh/w1awvao21...dzB8tHvVa?dl=0
Attached Files
File Type: xlsx sounding table.xlsx (40.8 KB, 7 views)
  Reply With Quote
Old November 2nd, 2019, 11:25 AM   #13
qwemx
Member
India

qwemx is offline
 
qwemx's Avatar
 
Join Date: Jul 2017
Location: UAE
Posts: 119
Today i took the values from the module when it was at bottom and at top and also at the point where the surface area of the tank changes

I also created a block in ladder to do calculations all details are in attachment please see

pot is reading 0 to 4.22 volts dc because this pot is not the exact replacement of the required pot however i am using the INT values from the module and not the dc values to make calculations
https://www.dropbox.com/sh/w1awvao21...dzB8tHvVa?dl=0

Last edited by qwemx; November 2nd, 2019 at 11:29 AM.
  Reply With Quote
Old November 2nd, 2019, 07:30 PM   #14
SD_Scott
Member
United States

SD_Scott is offline
 
SD_Scott's Avatar
 
Join Date: Feb 2006
Location: South Carolina
Posts: 168
I used to work in a lot of tank farms in the oil industry and the tanks are not uniform. We had 40,000, 80,000 and 250,000 barrel tanks and other sizes. We had what are called "strapping tables". They basically measure the tank diameter at different heights. The tanks had gauges that used a steel tape to measure the liquid level, and just did a look up and temp compensation etc.
  Reply With Quote
Old November 3rd, 2019, 06:06 AM   #15
daba
Lifetime Supporting Member + Moderator
United Kingdom

daba is offline
 
daba's Avatar
 
Join Date: Jul 2004
Location: uk
Posts: 4,701
Always going to be hard work....

Using "look-up" tables of height versus contents - how many points do you include ? The more you put in, the less the potential errors when interpolating between the upper and lower figures.

Using tank dimensions - how many tanks have the exact design dimensions ?


By far the easiest way, if it can be achieved in your case, is to put the tank on load cells and measure weight. A simple calculation can then be done to convert the weight to volume, based on the density of the contents, and temperature.
__________________
___________________________
ControlLogix & SLC Training
a-b train ltd.
abtrain@tiscali.co.uk
www.abtrain.co.uk
tel: 07506 73 9999
nil illegitimi carborundem


  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Omron PLC/Parker HMI tags ccathey LIVE PLC Questions And Answers 2 May 30th, 2017 12:36 AM
Volume of a horizontal tank go_bears LIVE PLC Questions And Answers 6 February 28th, 2009 04:38 PM
Analog Output follow up BoxerBrats LIVE PLC Questions And Answers 33 March 21st, 2005 11:00 PM
E-series HMI and Modems The_Wanderer LIVE PLC Questions And Answers 5 February 25th, 2004 10:46 AM
volume of horizontal tank missionmike LIVE PLC Questions And Answers 8 October 27th, 2002 01:32 PM


All times are GMT -5. The time now is 05:38 AM.


.