Powerflex 525 ethernet messaging to SLC or CMORE

So I have read and read and found little on this through forums and other research. I figured I would share it while its fresh in my mind. The first portion of this pertains to the now much outdated SLC 500 series. The second specifically CMore HMI's.

First scenario client asked to have said machine run on existing plc; outdated SLC 5/05. Subject making the new Powerflex 525 communicate via the plc and take frequency commands from the plc. The following must be done in order to accomplish this.

1. Make new File in program
2. Add 2 new Integer files, the first containing at least 156 integers. The second containing at least 3 integers.
3. following in ascii text the timers, integers, bits and IP addresses are examples do not assume entering this would result in just working!
rung 1:XIC B3:3:0/1 XIO T4:28/DN TON T4:28 timebase:0.01 preset: 800

rung 2:XIO T4:28/DN MSG Write 500CPU Local Control Block [N11:0] MultiHop( SLC:1->ENET:"10.96.104.2" ) This controller [N12:3] Target Device [N42:3]

rung 3:XIO T4:28/DN MSG Write 500CPU Local Control Block [N11:52] MultiHop( SLC:1->ENET:"10.96.104.2" ) This controller [N12:0] Target Device [N41:0]

rung 4:XIO T4:28/DN MSG Write 500CPU Local Control Block [N11:104] MultiHop( SLC:1->ENET:"10.96.104.2" ) This controller [N12:2] Target Device [N41:2]

The rest of the rung writing your logic and then writing a MOV command and sending it to N12:2
MOV source 3900 dest N12:2

In the above example of the MOV statement the source would equate to
39 hertz


The same can be done if you are wanting to route the frequency from the HMI specifically a CMORE which this was done on. Your MOV statement would read as the following example.

MOV source HMI NUMERIC ENTRY PUSHBUTTON N7:1 dest N12:2
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Detecting PowerFlex 525 Ethernet Comms Fault papacroft LIVE PLC Questions And Answers 7 April 19th, 2020 09:06 PM
AB PowerFlex 525 + Ethernet AgustinR LIVE PLC Questions And Answers 8 March 10th, 2015 12:49 PM
Powerflex 525 Detecting Loss of ethernet connection DAnderson LIVE PLC Questions And Answers 1 December 29th, 2014 01:30 PM
SLC 5/05 Ethernet Connections OkiePC LIVE PLC Questions And Answers 8 February 15th, 2010 03:52 PM
SLC 5/05 Ethernet RSLinx Driver Communication Setup PLBoudette LIVE PLC Questions And Answers 5 September 28th, 2007 11:14 AM


All times are GMT -4. The time now is 09:46 AM.


.