AB Logix IO module errors; end cap missing?
TJS
Oct 2004
Ohio, US
25
Can a lack of a right hand end cap in a Compact Logix plc rack cause all the modules to be faulted? I have not been able to get any of my IO cards to show up good, they are always faulted (3 IF8's, 1 OF4CI, PA7 in middle, 5 IA16's, 2 OW8I's).
I uprated the firmware to 15.34 and RSLgx15.02 from 13.03 figuring the EDS files or something was the problem. I guess I was wrong. Tech support also told me this would solve it. I noticed late today the right end cap is missing. How about left CPU cap, dont see any electrical contacts there?
Thanks for the positive response. The image of the missing end cap just popped back into my memory from all of todays problems and I hope thats all thats keeping causing them.
Exactly. Right-side end caps for the Compact I/O bus has a termination network of resistors that allows the bus to work. It does not ever work without an terminating cap.
My 1769 l33er also shows minor fault end cap is messing.but Im already contacted the end cap and also check the lock and connection im using left end cap Not right. Right side I'm using CRR1 expansion cable.
Studio 5000 shows IO not responding and indicator blinking green. All modules have yellow triangle
What is the reason
When adding an IFM AL1322 IO-Link Master Module to a 1756-EN2T Ethernet Card on a 1756-L82E Controller, The Input and Output data file does not...
94
I have am trying to determine if I can use a 1756-IB16I (or some dc input equivalent) to handle a 24vdc input pulse frequency of 80 pulses per...
887
This is a file from a customer PLC. I believe my partner copied it from their SCADA computer and then went online with it using his laptop. That...
358
Hello All, Can you check the below configuration and tell me how to check the module status of modules in the secondary rack of a redundancy...
470
Hello all, I need to add a module in logix for an SMC pneumatic valve manifold specifically EX600-SEN3/4. The eds files I add crash the program...
621