1769sc-IF4IH requesting information for .HartFault
mehsham
Sep 2016
Toronto
I have configured ControlLogix HART card but it's my first time working with compact logix HART card.
Unlike ControlLogix card, in compact logix a ton of the attributes are hidden or not access. IE (PV, SV, TV, HART Fault).
I was able to use a base line program from SPECTRUM (1769sc-IF4IH card has been designed by them) and managed to get the PV, SV, TV to populate.
I am stumped with HART fault bit in compactlogix. In ControlLogix HART card, 4) .Hartfault but can be used when an instrument has faulted and covers many parameters. However with 1769sc-IF4IH card, the only bits that I think I could use are as follows:
- OS0-OS3 bit (when channel is out of service)
- U0-U3 bit (open circuit condition)
Please refer to section 6.2 in the user manual
https://www.spectrumcontrols.com/media/1418/0300215-03_a0-manual_1769sc-if4ih.pdf
I would really appreciate if you guys can identify a bit in CompactLogix HART card identical to .Hartfault.
The compactlogix controller is 1769-L36ERM and running 20.14 firmware. The Hart Card revision number is 3.1 Series A
your manual, on pg 73, Ch7 table 1 shows the comms fault/no device bit
If4ih0Packet0[X,0].HartChannelID.5
Thank you for your response Scott. It appears that this bit only comes on if there is communication issue with the end device. A more thorough test will be done when I am on site.
I’m not up to speed on HART however the 1769sc-IF4IH comes with a TechConnect support contract so that you don’t have to have a TechConnect account to get support from Rockwell on the product. If you can’t get what you are looking for from them you can Email Spectrum at “[email protected]”. If you do contact Spectrum let them know what your ticket number is from Rockwell (not required but helpful).
Thank you Firejo! Will do that if it comes down to this.
Hi, I am new to HART and am using 1769sc-IF4IH HART module with L30 PLC. I was wondering if anyone has set up or had experience with this HART...
1,680
Greetings everyone, hope the day finds you well. So I am working on a project where I will be using 16 Type J Thermocouples, as such I found this...
2,232
I wanted to tell a story about yesterdays experience for future help to others. I arrived to a site to check and change a program for a Natural...
1,463
Have a customer with a number of these modules installed. The newer ones work great, but the older ones (by older I mean heavily used, moved from...
2,258
I have a problem with 1769sc-IF8u module ver 1.1 and demo serial number. I already install the 2.0 profile of that module and also download the...
2,105