Hello,

I am going interface the Wonderware Intouch with SCADAPack RTU through Modbus.

I have the following IO counts.
Analog - 30
Digital - 60

I want to know whether the Development Studio 2017, InTouch Dev/RT 64 tags is sufficient for the above said IO counts or not.
 
30 + 60 = 90.

You have a 64 tag license.

90 is greater than 64.

So I'd say no.

BUT. It depends what you want to do with those digital inputs. If they're purely for display then you could pack them into a 16 bit unsigned int and use only one analog tag per 16 digitals in Intouch.

But as soon as you want to do scripting or alarms or historize values then that approach gets messy.

Personally I'd get the right size Intouch licence for the job which is the next size up.
 

Similar Topics

We had a power outage at a site and there are two machines that run their own instance of Wonderware Intouch 2017 SP3. With this power outage the...
Replies
12
Views
1,545
Dear Friends, I reinstalled wonderware intouch in the machine and ran backup (Communicating through RSLINX- NO DAServer). Our more than 90% tags...
Replies
1
Views
1,531
Hi all, This is my first System Platform 2017 install. Have done plenty of mods to existing 2014 R2 installs and know what I'm doing in terms of...
Replies
3
Views
5,028
Wonderware Intouch, Kepware timing issue with "simultaneous" writing of many tags I have an Intouch application coupled with Kepware that is...
Replies
17
Views
7,066
So a customer gave me a list of tags they want to import into Historian. The list was derived from an InTouch tag DB dump. The original...
Replies
3
Views
3,971
Back
Top Bottom