Daisy Chaining a 4-20mA loop

dcam

Lifetime Supporting Member
Join Date
Apr 2012
Location
Merced Ca
Posts
161
Last night I ran into three drives on the same speed control 4-20. I had never seen this before and thought multiple devices would cause inconsistent speeds? Was hoping for some info on this if anyone cares to chime in. Thanks in advance for this forum.
 
A 4-20 mA signal sends the same current to all devices in the loop. If the drive analog inputs are properly calibrated and the total load does not exceed the allowable load on the transmitting device all three should run at the same speed.
 
If these are sequential conveyors it is common practice to have each section a little faster than the previous.



If the 3 need to be monitored and constantly adjusted, then a single output control might not be good if the loads can vary on them.
 
Some devices also don't have isolated analog inputs (one leg tied to 0V or ground) which will also cause a problem if inserted incorrectly into a loop. There are 4-20mA loop isolators and retransmitters designed for dealing with this.
 
Last night I ran into three drives on the same speed control 4-20. I had never seen this before and thought multiple devices would cause inconsistent speeds? Was hoping for some info on this if anyone cares to chime in. Thanks in advance for this forum.

This is very popular in process industry where you want to have a readout of an instrument locally. So they stick a 4-20mA display in the loop. In fact, a lot of instruments that have a display on top do it by placing two different bits on the current loop, one to display another to measure.
 
There should be no problem providing the loop resistance is not too low, after all the current is constant through all devices so if the card is outputting 12ma this is same thru out the loop (it has to be ohms law) but it may not be 12ma because of the load, this will not be a major problem as any error could be calibrated out. Assuming all series loops are of the same type or loop powered and not grounded 2-4 units should not be a problem.
 

Similar Topics

Hello, Trying to figure out if I can daisy chain powerflex 525's without using RS-485 cables and just using cat5 to the ethernet ports. Each...
Replies
10
Views
4,957
Hi all, Wondering what is the preferred method for running power around the panel. For example when building a panel if you have 24VDC from a...
Replies
22
Views
8,001
I have three shipping lines with a bagger, printer, palletizer and stretch wrapper. The bagger and palletizer each have a hub. My preference is...
Replies
12
Views
8,807
First, I have lots of copper networking experience, but next to no fiber experience. I bought eight unmanaged network switches (8 x copper...
Replies
2
Views
1,944
Just wondering if this is a no-no. Just as a background i'm using Allen-Bradley RSLogix 5000 over Ethernet/IP with remote IO racks and 3rd Party...
Replies
1
Views
3,859
Back
Top Bottom