plc storereviewsdownloads
PLC training tools sale
Reply
Thread Tools Display Modes
Old June 9th, 2019, 04:08 PM   #1
sparkie
United States
sparkie is offline
Suggestions for a smart relay?
I'm considering a micro 810 for this purpose. It is an outdoor pit pump application with a single submersible 3 phase pump and two float switches (high level and low level) to start and stop the pit pump. Has anyone had these outdoors for a prolonged period? Look at about -15F to 115F ambient with no shade, so it will get pretty hot in that box. That falls well within the operating range of the controller.
There will also be an audio-visual indicator on alarm if anyone has any recommendations.
https://ab.rockwellautomation.com/Pr...llers/Micro810
Old June 9th, 2019, 04:47 PM   #2
kallileo
Greece
kallileo is offline
Why not to use a simple level monitoring relay?
Looks a very simple application.
__________________
automationofthings.blogspot.com
Old June 9th, 2019, 05:01 PM   #3
sparkie
United States
sparkie is offline
I'm not sure how a level monitoring relay will handle any alarming, but I was also asked to include the ability get run times at a later date. Seems the micro810 fits the bill, while being pretty tough. A programmable control was also specifically requested.
Old June 9th, 2019, 05:48 PM   #4
damica1
United States
damica1 is offline
The Micro810 "In my opinion" would be a perfect choice for this application.
I have used the 810 several times for outdoor remote applications and they are still working
flawlessly!
__________________
David M. Camp
Unlocking the power of IOT in Oil & Gas!
Old June 9th, 2019, 05:58 PM   #5
geniusintraining
United States
geniusintraining is offline
geniusintraining's Avatar
If you want to get fancy how about a 820 then you can email the alarm? I have not used the email on them yet so not sure how much of a pain it is to setup.
Not sure on the temp, I try and stay about 70 deg, has not worked out lately
__________________
www.PLCCable.com PLC Communication Cables, PLC Trainers, MicroLogix, ControlLogix, Siemens, Allen Bradley and more...OEM and aftermarket supplies... Aftermarket 1784-U2DHP Allen Bradley USB to DH+, new USB to 485 modbus
Old June 9th, 2019, 06:14 PM   #6
sparkie
United States
sparkie is offline
flawlessly!
Fantastic damica1. That was what I was hoping to hear. Just for fun, here is one of the reasons it is getting a programmable controller:
https://i.imgur.com/TPnH4Iy.jpg
Old June 9th, 2019, 10:30 PM   #7
JeremyGranado
United States
JeremyGranado is offline
the 810 is ok but i prefer the 820. Just In case you want to more in the future
Old June 10th, 2019, 06:58 AM   #8
BITS N BYTES
United States
BITS N BYTES is offline
IDEC Smart Relay for me.
http://us.idec.com/Catalog/ProductSe...ammable_Relays
Old June 10th, 2019, 12:53 PM   #9
Rson
United States
Rson is offline
The micro 810 sounds like a great fit.
I’d suggest you get the LCD screen with it. I’ve done similar applications for motor testing with a micro 810 where they wanted run times / number of cycles /etc included. I used the LCD screen, to make a simple HMI that displayed all of said data and on the screen and the buttons allow resetting counters/etc without having to log on. (keep in mind, I did this back with V2 of CCW software – so I’m sure there are much better features at V12)
If you think they want to constantly check/change data, I’d go for a micro 820. I haven’t had a chance to do a ton with one yet, but I know the micro 820 allows the use of an SD card, so you can do actual data logging on that. Also, you can send files to/from the customer to load on the SD card and when they plug it in and power on the plc, it can read timer values/etc from the data on the SD card to adjust settings.
The micro 820 also has a remote LCD similar to the 810 but a little larger, and it can be mounted into the panel (unlike the micro 810 where the LCD must be on the controller)
Should be sub $200 for the micro 810 with LCD and programming port. I’m thinking around $400 for the micro 820 with LCD.
Old June 10th, 2019, 04:44 PM   #10
jraef
United States
jraef is offline
jraef's Avatar
I've been through this exercise before. The Micro800 line is rated for up to 55C ambient (131F) and down to 0C (+32F), as are manyt of the standard "smart relay" products. The only one I know of that's better is that Siemens has a "SIPLUS" version of their LOGO! smart relay that is extended to 60C (140F).
The Idec SmartRelay product is actually the Siemens LOGO! that Idec brand labels FROM Siemens (not the other way around as most people assume). But Siemens does not let Idec brand label the SIPLUS version with the higher temperature rating, so theirs is 55C like the standard LOGO! unit..
All of the other smart relays I have looked at are either 40C, 50C or 55C max. None of them are rated for operation at below 0C (they are rated for storage at down to -20C but not operation) however that's easier to deal with by just using enclosure heaters.
Old June 10th, 2019, 05:18 PM   #11
BITS N BYTES
United States
Really DON'T care whether Siemens manufacture Smart Relays for IDEC or Vice Versa. The IDEC software is IMHO way easier and simpler to use for the average programmer than bloated and over complex SIEMENS application.
My 2 cents
Old June 10th, 2019, 06:06 PM   #12
diat150
United States
diat150 is offline
check out the automation direct click. Software isnt bad, much better than Idec or siemens IMHO. I havent fooled with CCW in years but my experience with it was terrible. It has the same temp rating as the micro800.
Old June 12th, 2019, 09:10 AM   #13
Cow
United States
Cow is offline
We would also use a Click.
Reply
Bookmarks
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump
The "Imaginary Relay" Problem, Part-1 of 2 Terry Woods LIVE PLC Questions And Answers 17 February 13th, 2018 04:43 PM
Advice on a smart relay danw LIVE PLC Questions And Answers 6 June 24th, 2016 12:58 PM
Pause Zelio Smart Relay Timer jad51 LIVE PLC Questions And Answers 3 March 12th, 2013 01:54 AM
Choosing relay and PLC output card Adenitz LIVE PLC Questions And Answers 17 February 19th, 2010 03:57 AM
Quick Question About Siemens Smart Relay jivey1026 LIVE PLC Questions And Answers 4 February 17th, 2010 06:03 AM